0-10v dimming

Discussion in 'C-Bus Wired Hardware' started by cass123pugh, Sep 2, 2009.

  1. cass123pugh

    cass123pugh

    Joined:
    Sep 2, 2009
    Messages:
    2
    Likes Received:
    0
    Location:
    Telford
    Hi
    Can you please help, How many ballasts can you get on one 0-10v dimming unit
     
    cass123pugh, Sep 2, 2009
    #1
  2. cass123pugh

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    It depends on the ballasts, in particular how much current they draw from the 0-10V control input.

    The 5504AMP can source 2.5mA per channel, so if your ballasts draw, say 0.25mA, then you could have 10 per channel.

    Nick
     
    NickD, Sep 3, 2009
    #2
  3. cass123pugh

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The short answer is that it all depends upon your ballasts.

    As can be seen on the Specifications page of the Installation Instructions for the unit, it can source 2.5mA per channel and it can sink 8mA per channel (at 10V, worst case).

    What that means is, for example, if your 0-10V ballasts source 0.5mA, then you can connect 16 of them to a channel. If your ballasts source 1mA, then you can connect 8 of them per channel.
     
    Newman, Sep 3, 2009
    #3
  4. cass123pugh

    cass123pugh

    Joined:
    Sep 2, 2009
    Messages:
    2
    Likes Received:
    0
    Location:
    Telford
    0-10v

    Thank you for your help on this
     
    cass123pugh, Sep 3, 2009
    #4