1-10V Dimmer and wiring question

Discussion in 'C-Bus Wired Hardware' started by walkeraj, Feb 4, 2010.

  1. walkeraj

    walkeraj

    Joined:
    Jan 5, 2007
    Messages:
    25
    Likes Received:
    0
    I wanted all my CBUS units powered from their own MCB and a particular RCD.

    Question is, if I have the 1-10V unit hanging off this MCB and RCD and connected to a 1-10V PWM LED driver whose supply and neutral is on a different RCD will this be a problem causing a trip?

    Would the control circuitry in the 1-10V device be electrically isolated from the driver circuitry and not expecting to share grounds, have I explained this right?

    Or to make this work would the cbus 1-10V unit have to be powered from the same RCD as the 1-10V dimmer it is to be connected to?

    Not wired any 1-10V before, is solid CAT-5 ok, or bell wire or is T&E best?
     
    walkeraj, Feb 4, 2010
    #1
  2. walkeraj

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    It shouldn't be a problem...

    The output stage of the C-Bus Analogue Output unit is powered from a transformer, so it's isolated from mains. The 0V connection is however referenced to Earth via a high impedance.

    The main issue with 0-10V is voltage drop if you are using long runs or sinking/sourcing a lot of current in your control circuit (this is one of the reasons digital systems like DSI and DALI were invented).

    CAT5 strikes me as a bit on the small side, but it would probably be OK for a short run (from the wire size point of view - regulations and/or good practice are another matter).

    Nick
     
    NickD, Feb 5, 2010
    #2
  3. walkeraj

    walkeraj

    Joined:
    Jan 5, 2007
    Messages:
    25
    Likes Received:
    0
    maybe some bell wire would do it then or does this present the same problem as with cbus cabling having to be pink entering mains enclosures,

    Suppose I could use some 1.0mm T&E or maybe that would become confusing. I'll ask my electrician.
     
    walkeraj, Feb 5, 2010
    #3
  4. walkeraj

    Darpa

    Joined:
    Apr 30, 2006
    Messages:
    426
    Likes Received:
    0
    Location:
    Australia
    Bell Wire/ figure 8 cable would be the best way, however your electrician will have to maintain segregation requirements within a switchboard. Using pink cat5 wouldnt be a good idea, nor would T&E, as it would be too easy to confuse them later on with the cbus network or mains cables.

    If you are planning to run multiple 0-10v channels, you would probably be best going with a decent multicore cable, or if you're just running a single channel, then a double-insulated twin core cable, or speaker wire, would be a better way to go.
     
    Darpa, Feb 5, 2010