    Hi,

    Scenario:
    You have >2 DALI networks in an installation, but it can be part of 1 C-Bus network.
    1) Would you be able to address DALI fittings individually, if needed & how would it be done?

    OR

    2) Would you need network bridges to create multiple C-Bus networks and address the DALI networks with max. 2 DALI networks per C-Bus network.

    I know DALI groups and scenes can be addressed, but assume individual DALI addresses need to be addressed.

    Thanks,
    Brodsky
     
    brodsky, Jun 6, 2012
    #1
  2. brodsky

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    There's nothing stopping you having several DALI gateways on a single C-Bus network. If you run out of address space you can use an additional C-Bus Application Addresses for the subsequent DALI networks so that you don't get a clash between the DALI networks.
     
    Newman, Jun 7, 2012
    #2
  3. brodsky

    brodsky

    Joined:
    Mar 10, 2005
    Messages:
    138
    Likes Received:
    0
    Thanks Newman,

    Did not think of that. Will try it.
     
    brodsky, Jun 7, 2012