    I have a job where there will be 240v Siemens AC dampers.
    Is there any reason why i couldn't use a shutter relay per zone?

    I would use change over relays but i will end up having 3 spare channels on one of them!
     
    dannyd, Dec 1, 2008
    #1
  2. dannyd

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    I'm aware of some C-Bus installers using the shutter relay for damper control. You need to check if the damper is

    ...power to open and power to close

    -or-

    ...power to open and spring to close

    You will also need to check the current consumption of the damper... I would be surprised if it is greater than the rating of the shutter relay.

    BTW.... Lots of stock of the shutter relay about to become available

    cheers
     
    Conformist, Dec 1, 2008