    I have a 3 Phase supply that I need to monitor (current) on a permanent basis.. Up to 400A per phase. It needs to be a clamp style arrangement.

    I've seen the range of Fluke and Yokogawa devices, they seem over the top for my needs, lots of bells and whistles and starting around $2000..

    Does anyone have any thoughts on an alternative?
     
    Duncan, Jan 31, 2011
    #1
  2. Duncan

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,396
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    400A per phase is huge.

    Your trouble here is that most domestic style devices (designed for energy monitoring / user notification / how green is my house etc) are designed around max currents of about 40 to 80A per circuit.

    So you will probably in pretty specialised territory and may have no choice but to pay the big bucks.
     
    ashleigh, Feb 1, 2011
    #2
  3. Duncan

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Given that you're talking about seeing $2000+ device, I assume you're looking for something more than just a hand-held clamp meter that allows you to measure the current in individual phases?

    What about something like this or this?

    You might be able to use a much smaller unit by cascading CT's together. If you drop your 0-400A down to 0-5A then you'd only need a unit capable of 0-5A. You'd have to do a quick calculation to turn the reading into the real current however.
     
    Newman, Feb 1, 2011
    #3
  4. Duncan

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    CT's are what you will use.

    You then need to understand what type of output you need, 4-20mA, 1-5V, other and get the gear approriate for it.

    We have lots of CT's here on drives etc and monitor them 24x7 in the control system.

    Mick
     
    znelbok, Feb 2, 2011
    #4
  5. Duncan

    Duncan

    Joined:
    Jul 23, 2004
    Messages:
    925
    Likes Received:
    0
    Location:
    Salinas de Garci Mendoza, Bolivia
    Thanks Guys, a few options.. I'll let you know what we go with.
     