    Hello!

    Does this unit have up-to-date installation instructions as any other c-bus product? Where may it be downloaded from?
    Consider this unit to be included in c-bus installation. Does it supports 3-phase connection (3P + N) and proper power calculations? How the wiring should be done in this situation?
     
    p0rt3r, Mar 16, 2012
    #1
  2. p0rt3r

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The Installation Instructions aren't on the web anywhere however the product brochure, which includes a wiring diagram, is available here.

    The unit can measure current in up to 4 circuits and connections are by 4 separate split-core current transformers.

    The unit is a Current Measurement Unit, not a full-house power measurement unit. It does not have a voltage connection and can therefore not make a measurement of absolute power or power factor. It can be configured to broadcast power readings instead of current by specifying a nominal line voltage in the set-up of the unit.

    There is another thread that gives more details about the units operation here. I also suggest that you have a look at the UI in Toolkit to familiarize yourself with the unit.
     
    Newman, Mar 17, 2012
    #2
  3. p0rt3r

    Brendan Rogers

    Joined:
    Aug 3, 2004
    Messages:
    124
    Likes Received:
    0
    Last edited by a moderator: Mar 17, 2012
    Brendan Rogers, Mar 17, 2012
    #3
  4. p0rt3r

    p0rt3r

    Joined:
    Dec 16, 2010
    Messages:
    51
    Likes Received:
    0
    Location:
    Moscow
    Thanks. As I understood for the 3-phase connection I need 3 current trasformers installed on the 3 phase wires each. After that I can sum the 3 broadcasted values (current or mathematically calculated power) in software, and this will be the total consumption. Am I right?
     
    p0rt3r, Mar 19, 2012
    #4
  5. p0rt3r

    p0rt3r

    Joined:
    Dec 16, 2010
    Messages:
    51
    Likes Received:
    0
    Location:
    Moscow
    So what about my suggestions? Is the current unit suitable for the 3-phase connection?
     
    p0rt3r, Mar 22, 2012
    #5
  6. p0rt3r

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    If you have a device in your network that can calculate the 3-phase power from the 3 individual current readings and you make some assumptions about the line-to-line voltage and power factor, then in theory you can use the CMU to measure 3-phase power. The 3-phase total current is not simply the sum of the three line currents. A calculation is required.
     
    Newman, Mar 22, 2012
    #6
  7. p0rt3r

    p0rt3r

    Joined:
    Dec 16, 2010
    Messages:
    51
    Likes Received:
    0
    Location:
    Moscow
    That's why there is the question. Assume I have 3 CTs installed on 3 phase lines plus CT on the neutral. In software I can get 3 phase currents and calculate each phase power independently with theoretical voltage and power factor. By the way, can I do that?
    Then I can sum these 3 calculated values of phase power to get the total power of a 3-phase system. I calculate sum of scalar values (power), not the vector ones (currents).
    Does the power widget itself support such calculations? Or at least I will get 3 graphs with 3 phase power values separately.
     
    p0rt3r, Mar 22, 2012
    #7
  8. p0rt3r

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Well, it depends.

    If these 3 circuits are wired as three independent circuits that just happen to be on different phases, and they are metered independently, then you can treat them independently. If, however, they are wired to a 3-phase load then you need to consider them as a whole.

    In general, you cannot calculate the power in each phase independently and add them up because for perfectly balanced loads there is no current flowing through the neutral, whereas for a single phase circuits the full load current flows through the neutral. Unbalanced 3 phase loads also result in some current flowing through the neutral, the amount of which is related to the degree of imbalance between the phases.

    The Wiser widget does not support these calculations. You can monitor them separately in 3 widgets. A better approach would be to calculate your 3-phase power and re-broadcast the result back on the Meausrement application as a kind of virtual power meter. Then configure your Wiser widget to look at this virtual power meter data and not directly from the broadcasts coming from the current measurement unit.

    bmerrick posted about how to do this, combining the data coming from 2 measurements into a single measurement.
     
    Newman, Mar 22, 2012
    #8
  9. p0rt3r

    p0rt3r

    Joined:
    Dec 16, 2010
    Messages:
    51
    Likes Received:
    0
    Location:
    Moscow
    Thanks for the virtual meter idea. Will try that.
     
    p0rt3r, Mar 22, 2012
    #9
  10. p0rt3r

    poldim

    Joined:
    Dec 7, 2010
    Messages:
    166
    Likes Received:
    2
    Location:
    San Francisco, CA
    Is this UL'd and available in the US? If not, any such plans?
     