    Folks,

    I have a suspicion that my last post on this got buried. This is what I was asking:

    I have measured the voltages between +24 and the device inputs and I'm seeing 18 to 21 approx.

    I have measured the current between +24 and one of the device inputs and I'm seeing 22.5mA - which now leaves me confused as to the whole concept of 4-20mA !

    Still completely clueless! Thanks.

    Nick
     
    Last edited by a moderator: Mar 25, 2006
    NickLocke, Mar 24, 2006
    #1
  2. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    No better with Toolkit 1.3.0

    It had to be worth a try! Full install of Toolkit 1.3.0 and C-Gate. Project updated. Still exactly the same - all readings stuck on zero.

    I need some help please guys!!

    Nick
     
    NickLocke, Mar 27, 2006
    #2
  3. NickLocke

    RatDeSewer

    Joined:
    Sep 24, 2004
    Messages:
    39
    Likes Received:
    0
    Location:
    Henley Beach
    RatDeSewer, Mar 27, 2006
    #3
  4. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    E/mail sent to Support

    RDS, thanks for your guidance. I am in the UK, so I have sent an e/mail to [email protected]:

    Let's see where we go from here.......

    Nick
     
    NickLocke, Mar 28, 2006
    #4
  5. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    Onwards......

    A prompt initial response:

    .....to which I have replied:

    Hopefully I will get a response to that when you Aus chaps get out of bed tomorrow.

    Nick
     
    NickLocke, Mar 29, 2006
    #5
  6. NickLocke

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Hi Nick, and any other users of the 5504GI,

    I'm sorry to say that CIS engineering don't agree with the diagnosis of a firmware fault. There is some other defect with Nicks unit, and returning it for repair is appropriate.

    Can other users of the 5504GI please *not* assume that every one of them should be returned for some magical firmware change. If you have one and it does what you want, please leave it alone.

    Thanks
     
    ashleigh, Mar 29, 2006
    #6
  7. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    Update.....

    .....the 5504GI is on the way back to the UK distributor and a new unit has been ordered. So, hopefully, whether it is firmware or something else entirely, I should be up and running soon.

    Thanks to everyone that has helped.

    Nick
     
    NickLocke, Apr 1, 2006
    #7
  8. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    Progress Update

    I thought it would be worth an update on progress.

    In short, I am still waiting for a replacement or updated 5504GI.

    Apparently, my supplier is still waiting for something to arrive from Australia.

    So, it has only been seven weeks so far.......
     
    NickLocke, May 20, 2006
    #8
  9. NickLocke

    NickLocke

    Joined:
    Oct 27, 2004
    Messages:
    141
    Likes Received:
    0
    Eureka !

    I have finally received a shiny new 5504GI. It is connected to the same sensors as the old one, so all 4-20mA. The difference is that ..... this one works!

    I still have some work to do on scaling etc, but I can now see "raw" values between 0 and 255 on all four channels -- much better than the fixed 0 that I was getting before.

    I suspect we shall never know whether the old unit was faulty, or whether I needed the latest firmware. Bottom line is, it's working!

    Thanks to everyone that helped.

    Nick
     