Aux Input Module - 12v Relay?

Discussion in 'C-Bus Wired Hardware' started by Ks04, Jan 22, 2020.

  1. Ks04

    Ks04

    Joined:
    Dec 28, 2019
    Messages:
    114
    Likes Received:
    10
    Hi There,

    I want to trigger some scenes from my alarm panel (Ie. Lights out on exit delay, Lights on on entry delay).

    I have an L5504AUX input, and PGM outputs on the panel that can be programmed. The PGM outputs on the panel are 12v outputs - will this work with the L5504AUX given they're isolated inputs? Or do I need some kind of dry-contact relay converter.

    Thanks
     
    Ks04, Jan 22, 2020
    #1
  2. Ks04

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,554
    Likes Received:
    180
    Location:
    Adelaide, Australia
    The 5504AUX has dry contact inputs so you cannot connect any voltage source to it. The simplest solution would be to drive a relay from the alarm panel and connect the relay contacts to the 5504Aux.

    It is possible to drive the 5504AUX from open collector drivers if you have a common earth (which the panel would have), but that is an advanced options and you would have to decide if you had the skills to attempt it.
     
    Ashley, Jan 23, 2020
    #2