Auxiliary Contacts of Pro Dimmers

Discussion in 'C-Bus Wired Hardware' started by wanricky, Oct 10, 2005.

  1. wanricky

    wanricky

    Joined:
    Sep 12, 2005
    Messages:
    219
    Likes Received:
    0
    Is there any reference for the use of auxliary contacts of the pro dimmer? Catalogue says the contacts close on thermal overload or overcurrent condition, but installation manual doesn't say that. We want to know the common use of the contacts, such as for E-Lighting or cooling fans...etc.
     
    wanricky, Oct 10, 2005
    #1
  2. wanricky

    UncleSam

    Joined:
    Sep 7, 2005
    Messages:
    53
    Likes Received:
    0
    Location:
    StateSide
    relay this message

    The Auxillary Relay on the 4,2 and 1 channel PRO series dimmers is not configerable by software. It is hardware/firmware driven and has normaly open contacts that are closed (ie the coil is powered) when mains is avalable to the unit, the relay will open those contacts if mains goes missing or the dimmer overheats and shuts down. The relay contacts are not rated for large switching currents they are designed to act a dry contacts to ,say, an emergency power back up or remote warning panel to advise that there has been a power cut or tripped breaker on the supply to that dimmer.
     
    Last edited by a moderator: Oct 12, 2005
    UncleSam, Oct 10, 2005
    #2