Blind Control Using 12 Channel Relay

Discussion in 'C-Bus Wired Hardware' started by conor1, Sep 16, 2009.

  1. conor1

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    Has anyone used a 12 channel relay to operate blinds? So far I have 1 channel on the relay dedicated to "Blind 1 Up" and 1 channel to "Blind 1 Down" - obviously I can't run the risk of having both channels operate at the same time otherwise I will damage the blinds...Anyone know of a way around this?

    I know there is now a C-Bus Shuter Relay available but just try getting them in Ireland :)

    Cheers,

    Conor
     
    conor1, Sep 16, 2009
    #1
  2. conor1

    brodricj

    Joined:
    Mar 27, 2007
    Messages:
    117
    Likes Received:
    0
    Location:
    Perth
    There is a CIS Application Note how to do this, and it has been discussed on the forum here also. You need 2 change-over relay channels per blind/shutter (or one change-over relay channel and one standard relay channel per blind/shutter) to build in the required interlock and delay function for motor control. I have the doc here somewhere and can email it to you (it's on public release). Or no doubt contact Clipsal Tech Support and they will send it to you.

    Actually I prefer this method over using the shutter relay. Pay attention in another application note (07-001-1) to using a mains rated 470nF capacitor across the motor terminals to save risk damage to the relay contacts. I bought the capacitor but didn't install it, and unfortunately the inevitable eventually happened (I think the inrush current welded a change-over relay contact closed!)

    EDIT: The Application Note for shutter control isn't on the CIS website, perhaps it can be posted there by one of our forum Clipsal operatives?
     
    Last edited by a moderator: Sep 16, 2009
    brodricj, Sep 16, 2009
    #2
  3. conor1

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Interesting - can you elaborate on why this is?

    The biggest thing that kills the changeover relay contacts in this kind of application is failure to enforce the delay between changing directions. If you are switching directions without stopping for ~0.5s, it's highly likely that the contacts will weld within a few cycles.

    Nick
     
    NickD, Sep 17, 2009
    #3
  4. conor1

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    There are three ways of preventing both channels from being on.

    One is to use a C-bus change over relay

    the other is to use software (ie PAC)

    The second is not highly recommended as the primary means of preventing both channels being on.

    The third solution is to use some external off the shelf change over relays (mains rated coil and contacts) and use two standard relay channels to drive the two change over relays. These will be much cheaper than buying a C-bus CO relay, but will obviously take up more room in the cabinet - and you still don't get the delay required (unless you get a fancy on with a delay make setting)

    Mick
     
    znelbok, Sep 17, 2009
    #4
  5. conor1

    Colin Smith

    Joined:
    Aug 3, 2004
    Messages:
    102
    Likes Received:
    1
    Location:
    Auckland, New Zealand
    I have achieved this when the changeover relays were not around using a C-Touch for the logic control. Eight individual roller blinds in one room with individual / group control. Happy to share the code.

    Using changeover relays would be safer.

    I have this little niggle in the pit of my stomach that someday, someone - knee high with little fingers will press the override buttons on the controller and lock individual relays to drive both ways at the same time.

    (Do not enter that room and whatever you do - DO NOT press those buttons to make the pretty lights come on.)
     
    Last edited by a moderator: Sep 17, 2009
    Colin Smith, Sep 17, 2009
    #5
  6. conor1

    brodricj

    Joined:
    Mar 27, 2007
    Messages:
    117
    Likes Received:
    0
    Location:
    Perth
    My gripe with shutter relay is the timer, the UP timer and DOWN timer must be the same value. And there's no possible fix available in Toolkit because this is a hardware limitation. When using CO relays you can configure different UP and DOWN timers.

    For example (this is how I like to setup shutter control). When using CO relays you can configure a short press (say 10 seconds) on the UP key to give you a number of interim shutter stop positions on the way to FULL UP, and configure a short press on the DOWN key to give you a longer timer action (say 30 seconds). In application this means a single short press UP shutter goes 1/3rd the way up, another short press UP it goes to 2/3rd the way up, and a 3rd short press it goes FULL UP. A short press DOWN at any point and the shutter will go FULL DOWN whatever position the shutter happens to be at. Also, long press UP or DOWN and the shutter will move in that direction until release.

    As far as I know you just can't do that with the shutter relay (i.e. set different times for UP/DOWN actions). There might be a way to do it using logic, if so that is beyond me.

    The thing I like about the shutter relay over using CO relays is the simplicity of the local toggle action. You just need to press the UP or DOWN button on the shutter relay for the shutter to do what you want. For local toggle using CO relays you really need to think about it to get the required action, and you risk doing something wrong i.e. impossible for WAF.

    For shutter relay v2 I hope you can build separate UP and DOWN timers into it!

    BTW. As for my welded CO relay contact. I had a 0.5 sec delay built in and got 12 months reliable service from it without the 07-001-1 capacitor, and then one day I didn't. I had the capacitor for 11 months and didn't install it. I wish I had :mad:
     
    Last edited by a moderator: Sep 17, 2009
    brodricj, Sep 17, 2009
    #6
  7. conor1

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    brodricj you can do what you want with a Shutter Relay using some careful programming in the key input unit. Try this:

    Shutter relay
    On the Failsafe tab, Set up the Shutter Relay so that the failsafe timer is 31 seconds.
    On the Global tab, make sure Level Translation mode is turned on.

    Key Unit
    - Global tab
    Program the Ramp 2 rate as 30 seconds
    - Key Functions tab
    Program the Up key as Ramp Recall 1, Retrigger Timer, Idle , Recall 2
    Program the Down key as Ramp Off, Idle, Idle, Recall 2
    - Blocks tab
    Program Recall 1 as 100%
    Program Recall 2 as 2%
    Program Timer 1 as 10 seconds
    Program the Expiry as Recall 2
    Tick the boxes to link the two keys to the correct block/group

    This will give you the following behaviour:

    • A short press, and any subsequent short presses, of the Up key will run the blinds in the open direction for 10 seconds each time (Note: Once the Shutter Relay thinks that the blinds are at the top of their travel any more presses of the Up key will not operate the relay).
    • A short press of the Down key will close the blinds completely. This will still work even if the blinds are stopped part-way.
    • A long press of either key will run the blind in that direction until the key is released.
    How this works:
    When you briefly press the Up key you get a Short Press key event followed by a Short Release key event. The Ramp Recall 1 event starts ramping the Group Address to 100% at the Ramp 2 rate (30 second rate). The Short Release key event starts the 10 second timer. When the 10 second timer expires it issues a Recall 2 which sets the level to 2%. Level Translation in the Shutter Relay unit interprets this as a Stop command. This opens the blind in 10 second steps.

    When you briefly press the Down key the Short Press of the key gives you the Ramp Off event which ramps the Group Address to 0% at the Ramp 2 rate (30 second rate). This closes the blind.

    When you press and hold the Up key the Ramp Recall 1 event starts ramping the Group Address to 100% at the Ramp 2 rate (30 second rate). When you release the key the Long Release event will issue a Recall 2 which sets the level to 2%. Level Translation in the Shutter Relay unit interprets this as a Stop command.

    When you press and hold the Down key the Short Press of the key gives you the Ramp Off event which ramps the Group Address to 0% at the Ramp 2 rate (30 second rate). This sets the blind closing. When you release the key (after holding it down for more than 400ms) the Long Release event will issue a Recall 2 which sets the level to 2%. Level Translation in the Shutter Relay unit interprets this as a Stop command.
     
    Last edited by a moderator: Sep 18, 2009
    Newman, Sep 18, 2009
    #7
  8. conor1

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Newman, Sep 18, 2009
    #8
  9. conor1

    brodricj

    Joined:
    Mar 27, 2007
    Messages:
    117
    Likes Received:
    0
    Location:
    Perth
    Newman, thanks very much. Yes, your configuration summary does ring a bell how I configured TK for shutter relay control but it didn't give me the functionality I had when CO relays were used for shutter control. I'll need to look at it again more closely and see where I might have deviated.

    Certainly something is weird because the LED's on the key unit don't always agree with what the shutter is doing. When I was using CO relays, the LED on the key unit would blink (in response to timer function) whenever the shutter was in motion, and that made sense. When using the shutter relay, the LED on the key unit might remain on indefinitely without the shutter doing anything, or it might be off when the shutter is in motion, or it might be on when the shutter is in motion. I haven't been able to nut out the logic of the key unit LED's when using the shutter relay. Key unit LED indications were self-evident when running timers with CO relays.
     
    brodricj, Sep 18, 2009
    #9
  10. conor1

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    thanks

    thanks everyone for your help ,after considering eveyones comments i decided to use shutter relays all working fine.
     
    conor1, Oct 12, 2009
    #10
  11. conor1

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Thanks for letting us know Conor. Always good to hear that something has worked out well.
     
    Newman, Oct 12, 2009
    #11