C-Bus Cables Proximity

Discussion in 'C-Bus Wired Hardware' started by Leigh, Jul 1, 2006.

  1. Leigh

    Leigh

    Joined:
    Feb 2, 2005
    Messages:
    75
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    C-Bus cables need to be kept clear of 240v by 150mm when running parallel and 60mm when crossing.

    Is there any problem with running C-Bus cables adjacent to either telephone cables or home data network cables? I was thinking of running them through a common conduit in some locations.
     
    Leigh, Jul 1, 2006
    #1
  2. Leigh

    RossW

    Joined:
    Oct 10, 2005
    Messages:
    118
    Likes Received:
    0
    Telstra get funny about anything else being in the conduit with "their" cable, but from a purely technical (rather than regulatory) viewpoint, there is no problem running tv/video/network/phone/security cables with c-bus cables.

    I believe there are two problems with running mains wiring and cbus together - one the regulatory issue of SELV and LV together (although C-Bus cable insulation is I believe, rated appropriately to achieve compliance in that regard), and the issue of spike/noise induction in the c-bus cables. (Although, being all twisted pair, the common-mode noise should cancel leaving minimal impact).
     
    RossW, Jul 2, 2006
    #2