    Hi,

    Connecting via the CNI of the WISER.

    Having trouble getting the diagnostic tool to connect to the C-Bus when using the TCP/IP C-Bus connection. I have put in the correct IP address and port as I have the toolkit working on the same machine with the same details. It comes back with the message "CNI not found at IP address 192.168.2.2. (which is the IP I have fed in with the port of 10001.) When I do a scan with the IP Config utility it picks up these details as well. The C-Gate service is up and running (as I can connect via toolkit 1.12..). In the "Receive Data" panel it has a message of ".... *** connection already in use <CR>". I closed toolkit/PICED.

    Any suggestions please ?
     
    Derrick Bingham, Aug 20, 2012
    #1
  2. Derrick Bingham

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You need to put in the IP Address of Wiser, not the IP Address of its CNI.
     