C-Bus toolkit - Units not responding

Discussion in 'C-Bus Wired Hardware' started by mcsortan, Aug 18, 2014.

  1. mcsortan

    mcsortan

    Joined:
    Mar 16, 2013
    Messages:
    47
    Likes Received:
    0
    Location:
    adelaide
    I have an issue whereby I get about 6 - 7 units on my network coming up with "unit not responding" when I do a Network scan with toolkit.

    I have 31 devices on my network, one burden and 3 clocks

    Toolkit says I'm using 504ma of 520ma total from my power supplies and the units have a network voltage of between 30 and 31v

    The units that read "unit not responding" can generally not be accessed for programming.

    Everything functions ok though.

    All I can think is that I have marginal power to the network and need to add an additional power supply.

    Any help would be appreciated..!!
     
    mcsortan, Aug 18, 2014
    #1
  2. mcsortan

    tsman

    Joined:
    Aug 16, 2013
    Messages:
    62
    Likes Received:
    0
    Location:
    UK
    Check your wiring. If you have it backwards or bad cabling then it can appear on the network scan as something unknown at that address but fail to actually scan properly or allow programming.
     
    tsman, Aug 19, 2014
    #2