    The house I bought came with a fairly large fully operational c-bus network (52 units) with output units spread out in 3 different locations.

    I am worried that the cabling done by the installer is not very "pro".


    picture 1: c-bus ethernet (very long) cables running from one output unit in one location to another output unit in another location: the cables on one end are as pictured below (i suspect this is a crossover). What clipsal part should i use to clean this mess ?


    picture 2: it turns out 3 (very long) cables going to output units in "remote" locations are all connected to one single output unit in the main location, by having those 4 cables split and each color soldered together (picture 3). Is this proper (in terms of cabling) ? Is there a clipsal part to do this cleanly ?

    Thank you
     

    Attached Files:

    Last edited by a moderator: Apr 14, 2015
    nsa195, Apr 14, 2015
    #1
  2. nsa195

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Firstly - those cables are not ethernet.

    At least the installer used the pink cable.

    The C-Bus cable is not using ethernet, its running C-Bus. The pink cover shows that it's (1) C-Bus and (2) has a higher insulating rating than standard ethernet cable.

    BUT...

    That installation is a nightmare.

    You have safety ELV (C-Bus) running with bared and twisted cables right next to live mains. There is no segregation.

    I strongly suggest you get a proper C-Bus installer in to make it electrically safe as a matter of urgency.

    This install is a disaster waiting to happen, and whoever did it should be prosecuted.
     
    ashleigh, Apr 14, 2015
    #2
  3. nsa195

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,319
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi nsa195
    Ashleigh is correct.

    It really is time to get someone out there to check the installation and rectify the segregation.

    I've mentioned this to you before but I want to make it clear that CBus network wiring is not Ethernet.
    It may use the same cable and plugs but shares nothing else especially the wiring connections.

    I'd be horrified if a tradesman joined my Ethernet cables like that in a data enclosure but it's a whole lot worse since he has done that inside an electrical switchboard.

    You can read all about how it should be done here. http://www2.clipsal.com/cis/technic...ing2/cbus_control_and_management_system/basic

    Every single CBus component also has detailed installation instructions on CIS web site.
    It's a lot of reading I know but clearly some people who should be reading it aren't.

    You could read all that and definitely be much wiser than the electrician who wired that board but unless you are an electrician your really shouldn't be doing it yourself.
    It's not just some Cat5 cable for data, it is Cat5 cable stuffed into an electrical switchboard.

    I also agree that the electrician who did that work should probably be prosecuted.
    Perhaps you could investigate that path to having the repairs made.
    Or even better find someone with some CBus experience to fix the wiring and get you up and running with the programming.
     
    Last edited by a moderator: Apr 16, 2015
    DarylMc, Apr 16, 2015
    #3
  4. nsa195

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    I'll go a step further in brutal honesty.

    The ONLY REASON the regulators allow C-Bus inside an electrical switchboard (which is full of mains voltages that can kill you) is because there are no bare wires, and the PINK cable is both double insulated AND has a higher than normal insulation rating.

    So what's been done here is to:

    1. Break the double insulation right back to bare wires.

    2. Put the bare wires of C-Bus inside bits of crappy masking tape (not insulation, good for painting).

    3. Put all that right next to live mains.

    AND NOW because you know about it, AND have photographed it, AND placed that on a public forum. Then LEGALLY you know about the problem, have been advised that its a problem, so it you don't do anything about it this is negligence and if there is a fire caused by it YOU THE OWNER who knows about it is in big big poo. Your insurance won't cover you. You might be able eventually to sue the previous owner and/or installing electrician in the event of a disaster. Good luck there - years in court but you might need that as the only redress without insurance cover.

    So get it fixed, urgently. By a professional.

    It will cost you a lot to fix it. It will cost even more if your house burns down.
     
    ashleigh, Apr 17, 2015
    #4
  5. nsa195

    Mr Mark

    Joined:
    Jan 27, 2006
    Messages:
    323
    Likes Received:
    5
    Location:
    FNQ
    How about feeding the pink cables into a 30 series outlet enclosure (Part number 4PS31). Make sure they are fixed in, maybe cable tie and with no single insulation showing. Use an RJ45 socket in place of a switch and you have a C-Bus socket available at your board.
    Still, I agree with the others here and would strongly suggest getting someone qualified in to have a look. If this is the standard in the accessible board, what is the rest of the install like?
     
    Mr Mark, Apr 17, 2015
    #5
  6. nsa195

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    788
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    I agree and disagree with the comments posted in response.

    Firstly, I think it's a little unfair to paint a picture of gloom and doom on this installation. Yes, it is not legal and potentially dangerous but... it should not be an expensive exercise to fix and get it up to spec, so don't feel it will cost the earth to fix and try to do it yourself

    Engage a professional who will know how to make this legal and safe. I won't say what needs to be done (offer advice) but any reasonable installer should be able to tidy this up in an hour or two.

    BTW, the tape used does look like white electrical insulation tape, but the installation is still not legal or safe as Ashleigh has indicated.
     
    Last edited by a moderator: Apr 20, 2015
    Conformist, Apr 17, 2015
    #6
  7. nsa195

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,319
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi conformist
    I agree that the homeowner does not need to be alarmed excessively but this definitely does need to be fixed.
    Hopefully he will take the advice from everyone here.

    It's very disappointing to see such poor workmanship on the CBus install but I also think that making it much safer is not that huge a task.

    If the guy who did the wiring also did the commissioning it would be another good reason to get someone with some experience to look at it.
     
    DarylMc, Apr 17, 2015
    #7
  8. nsa195

    Ashley W

    Joined:
    Aug 4, 2004
    Messages:
    304
    Likes Received:
    3
    Location:
    Canberra
    Agree that this install is crap, but you raise an interesting point about separation.

    I had it put to me that even though C-bus carries ELV signals, it in fact should be treated as if the cable is LV (240v) due to the (lack of) isolation within relays and dimmers. Hence why C-bus should be using mains rated cable. So by rights it should be run with other LV cables, and should NEVER be run with data cable and the like.

    Must admit cannot find any specific reference to this, though DALI, which uses a similar principle of using ELV signals on a mains rated 'data cable' does quite clearly state the cable should actually be treated as LV and run as such.
     
    Ashley W, Apr 18, 2015
    #8
  9. nsa195

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,319
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi Ashley W
    I am not aware of any CBus installation instructions which suggest segregation from data cabling but there definitely are instructions to avoid running CBus cables alongside power cables.
    In the case of this installation it sounds like it is perfectly functional.
    But the segregation is poor and does need to be fixed.

    It's taking it to another level if someone was to suggest that a fault on the CBus network could potentially make the CBus cabling 240V and also incorporate a breach of it's mains rated insulation and the data cabling insulation at the same time.
    This is exactly why this installation needs to be fixed because the risk of 240V being applied to the CBus cables is high.
     
    Last edited by a moderator: Apr 19, 2015
    DarylMc, Apr 19, 2015
    #9
  10. nsa195

    Ashley W

    Joined:
    Aug 4, 2004
    Messages:
    304
    Likes Received:
    3
    Location:
    Canberra
    It is an interesting issue and one I don't think any regulation covers all that accurately.

    I mean to say from a separation issue, it is fine to run C-bus in a switchboard enclosure with 240V present so long as you use the pink C-bus cable. In fact you need to, to get to output modules etc. But in the next breath you need to maintain separation from mains. So begs the question is that cable then a SELV data cable, a power cable or something different?

    As mentioned DALI is similar in the electrical characteristics on the control cable, but is NOT considered to be an SELV cable and may be run with power and certainly shouldn't be run with data.

    So where is the difference.

    Buy yeah in this case it is very poor and having exposed terminations certainly goes against Clipsals own advice.
     
    Ashley W, Apr 22, 2015
    #10
  11. nsa195

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Somebody is confused with DALI.

    When a SELV cable / system goes INSIDE a product, the internal design has to meet stringent safety requirements including double or protective insulation, thickness of insulation, and a minefield of other fun things (pollution degree, material grade, surge class, and a more.)

    What you have been told is completely wrong. [BUT IS TRUE FOR DALI!.]
     
    ashleigh, Apr 27, 2015
    #11
  12. nsa195

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    You also need to have physical separation (ie segregation).

    It is a data cable. If you go through the what the data cable (and because of possible connection to telephone systems, telecoms...) regulations, its a data cable. The requirements are hard to dig up concisely, I had to do a 1 full day course on it before I really understood it.

    DALI has only single insulation from mains, AND DALI IS REQUIRED TO WITHSTAND A CONNECTION OF MAINS TO THE DALI INPUTS OF A PRODUCT.

    This means that DALI can NEVER be a safety system as it does not have a double insulation requirement. Nor a segregation requirement.

    DALI is frequently wired up using mains cable and can be indistinguishable on a site.

    And its quite normal in DALI installations for accidental connection of mains to DALI.

    Morals of the story:

    1. C-Bus aint DALI.
    2. C-Bus is SELV and must be treated as a safety, double insulated system all the way through from end to end.
    3. DALI aint C-Bus.
    4. DALI aint SELV.
    5. In wiring regs land, DALI is considered to be LV (just like mains power).
    6. In case some goose wired DALI to mains by accident, don't touch unknown DALI terminals and don't ever stick your tongue over them. It might be the last thing you do.
     
    ashleigh, Apr 27, 2015
    #12
  13. nsa195

    Ashley W

    Joined:
    Aug 4, 2004
    Messages:
    304
    Likes Received:
    3
    Location:
    Canberra
    Interestingly Clipsals own training material doesn't quite say that. What they say is using the pink cable inside a switchboard.

    So closer than normally would be allowed, meaning it isn't really the same as an SELV data cable, and practice is to keep as far apart and cross at 90 degrees for noise immunity, no mention of safety, which is the crux of data cabling rules. So about as clear as mud really.
     
    Ashley W, Apr 27, 2015
    #13
  14. nsa195

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,319
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi Ashley W
    This is my take from Introduction to CBus training manual.

    CBus cabling is classed as SELV.
    I can find no recommendation to separate CBus Cat5 from data cabling around the installation.

    A well laid out board will not have the pink cable in contact with mains cabling.
    I find this practically achieved by considering the following.
    Ensure the pink cable enters the left side of the board, keep the mains wiring to the right, one output unit per switchboard row, control breakers and RCD's to the right side of output units, that the board is of a suitable size and layout, other measures such as ducting and whatever else needs to be done to make it safe.
    At the end of these instructions is the quite critical requirement to anchor the CBus cables and the mains conductors within the switchboard so that they cannot move and inadvertently touch each other.

    Some bits from the manual

    A bit from a relay instruction sheet regarding bungs for the RJ45 sockets.

     
    DarylMc, Apr 27, 2015
    #14
  15. nsa195

    Ashley W

    Joined:
    Aug 4, 2004
    Messages:
    304
    Likes Received:
    3
    Location:
    Canberra
    Don't need to convince me, I've been working with C-bus since 1999 and been working in the communications industry since 1990.

    I only raised the question because it was put to me in the context of the electrical characteristics of DALI with the question why DALI treats the control cable as LV, whereas it seems C-bus it is SELV with some exceptions in the switchboard. I must admit I think the question is still very valid, especially in the context of the picture in the first post which we all agree is bad practice and dangerous.
     
    Ashley W, Apr 28, 2015
    #15
  16. nsa195

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    DALI is classed as LV because of single insulation from mains. [By definition, if its not SELV then it has to be the next step up, which is LV.]

    A SELV system must have double insulation or reinforced insulation.

    Refer to (at least) AS/NZS 60950.1, Information Technology Equipment - Safety.

    This is covered in this standard in gory detail. [Ditto a range of other standards which ultimately require the same thing.]

    The turning of standards into practical installation advice, as well as meeting what inspectors and other regulators wish to see is the job of the various guides. I'm not saying they are wrong, merely that they tell you WHAT to do, not WHY you must do it.

    DALI coming along in a C-Bus world has probably thrown some confusion into the works - they ARE NOT both SELV systems, THEY DO have different requirements to meet, and THEY MUST use different wire types to wire them up.

    For C-Bus, the issue of segregation in a switchboard is one of those things thats a grey area. If you have physical separation you should have no trouble with inspectors [do those exist any more?]. If you don't you may have an argument.

    The pink cable with its higher insulation rating means that IN THEORY you can run the pink cable right alongside mains as it has double insulation AND that insulation has the appropriate voltage rating.

    Voltage ratings for insulation is another whole can of worms, which the standard I referenced above covers in some detail. In summary though, in a switchboard the insulation must be good for 4000V. That seems over the top but it accounts for voltage surges. Normal blue ethernet / cat5 / cat5e / cat6 is only rated to 1500V which is why you CAN NOT use it in an electrical switchboard. [Even then you might be able to sometimes, provided you took extreme care in physical segregation, such ethernet must have large separation from mains and no crossovers. This is a separate topic where anything I write here must be qualified with "might" and "may" and you really need careful wiring practices, and I'm giving advice about it!]
     
    Last edited by a moderator: Apr 29, 2015
    ashleigh, Apr 29, 2015