CBus/ctouch system time

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by i-Home, Oct 19, 2009.

  1. i-Home

    i-Home

    Joined:
    Feb 18, 2008
    Messages:
    25
    Likes Received:
    0
    Location:
    Northern Ireland
    Yes, problem does occur with 4.8.3, as I found out after updating the ctouch firmware.

    When you say to use something other than the ctouch to set the time, what type of device would suit? And as I understood it the problem was that the ctouch is broadcasting the time around the system every 60 or 90 mins which in turn overwrites the time set by the DLT.

    Stephen
     
    i-Home, May 13, 2010
    #21
  2. i-Home

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    As far as I can tell, the problem only exists immediately after you manually set the time on a Colour C-Touch. After this, it will be fine, even if the Colour C-Touch is the time master.
     
    Darren, May 13, 2010
    #22
  3. i-Home

    i-Home

    Joined:
    Feb 18, 2008
    Messages:
    25
    Likes Received:
    0
    Location:
    Northern Ireland
    With me at least it seems to be that if the time is set with a DLT it only remains "correct" until the ctouch broadcasts the time to bring it back an hour.

    When this problem first occured last year it was the same, i.e. correcting the time using a DLT or the Date/Time of the ctouch only fixed the DLT displayed time until the ctouch broadcast took place 60-90 mins later.

    Very strange that it seemed to be cured on my system up until a few days ago. Nothing was changed recently that could have triggered this broadcast error.

    Stephen
     
    i-Home, May 14, 2010
    #23
  4. i-Home

    Thomas

    Joined:
    Nov 25, 2004
    Messages:
    252
    Likes Received:
    0
    Work-around?

    Hi Stephen / Darren,

    I followed this thread, as the time master management of the system is quite interesting to me.
    I'd like to make a suggestion which may be tried out. Since I have not had any report of this issue here, where we have no summer time offset, I am thinking that the issue may be related to that.
    Therefore I thought that loading the relevant project on the C-Touch without any summer time offset, might resolve the issue for now. If so, at least you only need to change the time twice a year.

    Could this work?

    Regards
    Thomas
     
    Thomas, May 14, 2010
    #24
  5. i-Home

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,400
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Sadly no.

    The problem is related to the way 2 pieces of software in the C-Touch talk to each other, and this interface gets exercised every time there is a date/time change made using the screen user interface.

    It will be fixed soon.
     
    ashleigh, May 15, 2010
    #25
  6. i-Home

    i-Home

    Joined:
    Feb 18, 2008
    Messages:
    25
    Likes Received:
    0
    Location:
    Northern Ireland
    Note that although you say the problem occurs when the ctouch date/time screen interface is used, I'm still having the issue after correcting the time using the DLT's.

    Anyway, hopefully the next PICED release will sort this.
     
    i-Home, May 15, 2010
    #26
  7. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    Any fix yet?

    I am having the exact same problem on a site in the UK which started happening around the start of May.

    This project has 3 networks (one a wireless) with 6 Colour touch screens accross the networks. Once you reset the time at one of the screens that screen will set the clocks accross the whole networks back one hour and then keep sending out the wrong time. If you change it back at a different screen it will be ok until it resends out the time and then it will set it wroing again.

    I have a nice long lists of logs if you guys would like them, let me know where to email to.

    If this has been fixed please let me know what it is as i've been pulling my hair out and only just found this thread today :eek:
     
    ______., Jun 8, 2010
    #27
  8. i-Home

    i-Home

    Joined:
    Feb 18, 2008
    Messages:
    25
    Likes Received:
    0
    Location:
    Northern Ireland
    Oddly, a day or so after my last post on this issue the time "corrected" itself for no reason, i.e. nothing was changed on the system but simply after a while the time went back to what it should have been.

    And now yesterday the time has changed back again, and nothing was changed this time either. As I use the DLT time read-out quite a lot I notice when it's incorrect quite quickly. As of yesterday evening the DLT times are 1 hr behind the actual and ctouch time.
     
    i-Home, Jun 9, 2010
    #28
  9. i-Home

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The problem is in our system as #19316. A fix for this will be included with the next release of PICED, but I can't say exactly when that will be.

    If you set the time with a different type of unit (black and white C-Touch or DLT), then things should work OK. You could also use the C-Bus diagnostic utility to send a date/time message onto C-Bus.
     
    Darren, Jun 9, 2010
    #29
  10. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    Can you give me any idea? Are you talk days, weeks, months :confused:

    How do you send that message from diagnostic untility. I was looking through it and couldn't find anything.

    Is this a problem only in the UK as so far iHome and myself are in the UK and i haven't seen anyone else asking about it in the forums? If so can CIS please update Tech support in the UK as i rang them and they knew nothing about it.

    Any idea on what is causing it to start happening?
     
    ______., Jun 9, 2010
    #30
  11. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    Are you saying your colour touch screens are showing the correct time but the DLT's aren't?

    My system the touch screens are displaying the wrong time. I have not looked at the DLT as the touch screen are the bigger problem for me. Strange thought if your touch screen is displaying the right time, while mine is not :confused:
     
    ______., Jun 9, 2010
    #31
  12. i-Home

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Assuming you're running Diagnostic Utility 2.0.0 and successfully connected to your network, go to the Time tab at the very bottom of the program. You might have to scroll to the right through the tabs using the arrows in the very bottom right hand corner of Diagnostic Utility. Once you've got your time entered (system time or otherwise), press the Transmit button.
     
    Newman, Jun 9, 2010
    #32
  13. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    And there is the problem newer version on Diagnostic needed. I was using 1.8.1 :rolleyes:
     
    ______., Jun 9, 2010
    #33
  14. i-Home

    Duke D

    Joined:
    Nov 20, 2008
    Messages:
    30
    Likes Received:
    0
    Location:
    Nashville, TN (USA)
    Still Having Touch Screen Time Issues

    I am still having similar time issues on our installation. 10 Touch screens (4 Color, 6 Mark II). Homeowner is reporting the system time shifts by 1 hour increments spontaneously. It sometimes shifts forward, sometimes backward. The shifts seem to be betwen 12 and 24 hours between events, but so far, they seems random. Homeowner has reported system has eventually shifted as far as 4 hours forward over several days.

    I made a site visit a couple weeks ago for a couple other issues and made double sure all 10 touch screens were on the same time zone, thinking this was perhaps the issue. Perhaps the time master was shifting to a device set to a different time zone? (if this was the case it would have been a 2-hour shift - as the job is 2 time zones from where I've done much of the programming). After the check, I got a call 3 days later - still having the same issue.

    On a couple instances when I was there, I set the time on a color touch screen and then hit 'OK'. About 10 seconds later the time would shift by an hour. On other occasions it would not shift. (Unfortunately, I did not have time to run a log to watch the time messaging.)

    The project has 4 networks. 2 of the networks have devices which can set the time; Touch Screens (color and MII on both networks), 9 DLTs on one network, 8 on the other, 6 Thermostats, and a Ness/Elk C-Bus interface for an Elk M1 panel.

    All programming has been done with Toolkit 1.10.9 and PICED 4.7.2.


    The homeowner is upset and I can't get him to run a log file to look for the culprit.

    Any suggestions?
     
    Duke D, Jun 9, 2010
    #34
  15. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    From what the guys here are saying it's not a singel device that is doing it but something to do with the colour screens for some reason send out the wrong time message. So don't spend time hunting down a problem device. I did but found the screen that was sending out the wrong time message was the screen I set the time correctly on. Then by changing the time at another screen it in turn started to send out the wrong time. Trust me it was a fun fault to find and work out :rolleyes:

    Now just hoping the permenant fix will be released soon
     
    ______., Jun 9, 2010
    #35
  16. i-Home

    i-Home

    Joined:
    Feb 18, 2008
    Messages:
    25
    Likes Received:
    0
    Location:
    Northern Ireland
    I get the feeling we're flogging a dead horse here as this problem in its various forms will hopefully be fixed with the next PICED release, which normally happens quite regularly.

    It's odd that I've only came across this problem with my own home install and none of the client installations. And perhaps even more odd that it has came and went a couple of times for no reason I know of. Certainly no-one else in my home fiddles with the units or times, so I'm certain no-one changed the time on the colour ctouch to make the unit broadcast the time change.

    And with my install, setting the correct time using a DLT is only a short-term fix. The ctouch overrides this after a short time. So IME setting the time with a DLT does not bypass the problem.

    When the problem is evident, i.e. the DLT times are 1 hr behind, the ctouch time is correct. As I've said before, simply going into the ctouch time/date page, not changing any values and then selecting ok, would make the ctouch broadcast the correct time. But this (as with the DLT setting) is only a short-term fix.

    Stephen
     
    i-Home, Jun 9, 2010
    #36
  17. i-Home

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    We have just released a service pack for PICED (V4.8.4) to address the problem with setting the time from Colour C-Touch.

    We believe that this should solve the problems people are having. We would appreciate any feedback regarding whether the update resolved all of the problems or not.
     
    Darren, Jun 11, 2010
    #37
  18. i-Home

    ______.

    Joined:
    Feb 4, 2008
    Messages:
    91
    Likes Received:
    0
    Location:
    UK - London
    I have just updated the 6 screen on my project that was having the trouble. I will update if the fault appears again.

    Do you know what caused this to start happening? And who to send the bill to :p
     
    ______., Jun 11, 2010
    #38
  19. i-Home

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The tool we use for building the C-Bus Module DLL (used in the Colour C-Touch and elsewhere) was updated a while ago. The tool vendor changed a default compiler option which caused a very slight change to the DLL interface. The change did not show up in our regression test harness (which performs over 500 tests on the C-Bus Module) because it was built using the same tool. It took quite a while to work out where the problem was coming from.

    In the end we did not have to make any changes at all to the code. We just had to change the compiler option back to what it was and re-compile.
     
    Darren, Jun 13, 2010
    #39
  20. i-Home

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    Time

    Hi ,
    I have a c touch which when I go to change time from touch screen it changes for a few moments then compiles logic and schedule and when complete reverts back to original time any ideas welcome .

    Regards Conor
     
    conor1, Oct 17, 2010
    #40
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.