Cbus Light sensor switching metal halide lighting

Discussion in 'C-Bus Wired Hardware' started by colmac, May 14, 2014.

  1. colmac

    colmac

    Joined:
    May 14, 2014
    Messages:
    3
    Likes Received:
    0
    Location:
    perth
    I am looking for some advice.
    I have installed a cbus light sensor to control a 4 channel relay for metal halide lights in a warehouse.

    I am getting a lot of nuisance switching when clouds pass over due to huge varations in lux levels. I have set a large margin already. I cant really set the margin any more otherwise the lights wont come on till too late at sunset. Is there anyway that i can set the relay or the sensor to delay the switch on as what i am experiencing is a sudden drop of below 200 lux for a short period of time due to heavy cloud which passes pretty quickly. Which instantly causes the lights to switch on and then off a few minutes later when the lux level rises back up to 500 plus. I am concerned that this is shortening the life of the lamps.
     
    colmac, May 14, 2014
    #1
  2. colmac

    Mr Mark

    Joined:
    Jan 27, 2006
    Messages:
    323
    Likes Received:
    5
    Location:
    FNQ
    Hello colmac.
    Do you have a touchscreen or PAC to run logic in?
     
    Mr Mark, May 14, 2014
    #2
  3. colmac

    colmac

    Joined:
    May 14, 2014
    Messages:
    3
    Likes Received:
    0
    Location:
    perth
    I have a PAC
     
    colmac, May 14, 2014
    #3
  4. colmac

    Roosta

    Joined:
    Nov 22, 2011
    Messages:
    560
    Likes Received:
    1
    Location:
    Australia
    Find a better spot for your PE cell..
     
    Roosta, May 14, 2014
    #4
  5. colmac

    colmac

    Joined:
    May 14, 2014
    Messages:
    3
    Likes Received:
    0
    Location:
    perth
    Its not the location of the sensor that's the issue. the whole warehouse experiences the same difference in lux
     
    colmac, May 14, 2014
    #5
  6. colmac

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,548
    Likes Received:
    178
    Location:
    Adelaide, Australia
    Create a group called, say, 'sensor disable'. Select this group in the sunset to sunrise function. Set the timer to say 10 minutes. Select the same group in the sensor enable/disable box and check 'disables'. When the light level goes low this will disable the sensor for the specified time.

    Disclaimer: I haven't actually tried this :)
     
    Ashley, May 14, 2014
    #6
  7. colmac

    Roosta

    Joined:
    Nov 22, 2011
    Messages:
    560
    Likes Received:
    1
    Location:
    Australia
    Ok so at what approx lux at sunset do you wish for the lights to come on at?
    200 is still pretty bright..
    The australian standard for warehouses is 150 lux on the workplane..
    Depending on the location of the sensor and the levels it is presenting i would be setting it to on/off control with 155 lux with a margin of 10%.. So the load will get turned on when lux drops below 140 lux and will turn off again at when light level exceeds 170 lux..
     
    Roosta, May 14, 2014
    #7
  8. colmac

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    458
    Likes Received:
    35
    Location:
    Sydney
    Same as others I haven't tried this but it may help.

    Rather than using 'Light On/Off', try using the 'Light Level' option. Then on your relay change your 'turn on threshold' to 75 or 100%.

    As the light level option ramps the level rather than just turning it on and off it should give you a delay in the on and off of the fixture. The delay will be dependent on the light change and the level of your threshold. By playing around you may find a good delay time where, within the time it takes to get to 75% the clouds have passed and it starts to ramp down again without turning on the lights.
     
    jboer, May 15, 2014
    #8
  9. colmac

    Mr Mark

    Joined:
    Jan 27, 2006
    Messages:
    323
    Likes Received:
    5
    Location:
    FNQ
    Another option, using logic:
    Use a group, maybe called "Lights on by sensor" in the light level sensor.
    Use a group, "Lights" on your relay channel.
    Code:
    // Sensor calls for lighting to be turned on.
    once
     (GetLightingState("Lights on by sensor") = ON) then
    begin
     TimerSet(1, 1); //Start timer.
    end;
    
    // Turn lights on if still needed after 30 seconds.
    once
     TimerTime(1) > 30 then
    begin
     SetLightingState("Lights", ON);
     TimerSet(1, -1); // reset timer
    end;
    
    // Sensor calls for lighting to be turned off.
    once
     (GetLightingState("Lights on by sensor") = OFF) then
    begin
     SetLightingState("Lights", OFF);
     TimerSet(1, -1); // reset timer
    end; 
    
    I'm tapping this one out on the iPad , so syntax may not be 100% correct but hopefully you get the idea. :)
     
    Last edited by a moderator: May 15, 2014
    Mr Mark, May 15, 2014
    #9
Ask a Question