    using changeover relay on roller blinds with built in limmits working fine but has seemed to have stuck on change over after quick succession of uses
    regards conor.
     
    conor1, Aug 3, 2007
    #1
  2. conor1

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne

    Are you using only 1 channel ?? (I hope not !) (the delay between up and down will kill the motor !! or weld the contacts on the relay !)

    Or are you using 2 channels one up and one down and wired with interlock


    Charles
     
    Last edited by a moderator: Aug 3, 2007
    Charlie Crackle, Aug 3, 2007
    #2
  3. conor1

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    hi charles ,no using 4 channel change over relay and it has been working fine for aprox 4 weeks .
    regards conor
     
    conor1, Aug 3, 2007
    #3
  4. conor1

    Nathan

    Joined:
    Aug 3, 2004
    Messages:
    161
    Likes Received:
    0
    i think there could be a problem with these. i recall a thread using capacitors across the channels. Ive used hundreds of these and only in the last 6 months were are getting sticking contacts. might be one for the qa guys to have a look at. ive either sent them back are a light tap has fixed the problem. the motors are the standard somfy so theres no change in the motors we are connecting them to
     
    Nathan, Aug 5, 2007
    #4
  5. conor1

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    How are you wiring it? Can you provide a diagram?

    Nick
     
    NickD, Aug 5, 2007
    #5
  6. conor1

    eleroAustralia

    Joined:
    Nov 12, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Germany
    By the sounds of it the motors have been connected to 1 relay output and using NC and NO contact of the relay to switch the motor (easily identified if you cannot stop the motor halfway), in the worst case, even parallel wired.
    If this is the case:
    If directions have been changed while the motor was moving the resulting Voltage (240V Supply plus overlaying feedback from capacitor which is inside the motor) may have welded the contacts together!
    Sometimes a "pad on the back" (Of the relay unit) loosens the contacts again, but I certainly would change the connection if it is connected as I described it above! Otherwise the motors will be damaged over time.
     
    eleroAustralia, Aug 7, 2007
    #6
  7. conor1

    Nathan

    Joined:
    Aug 3, 2004
    Messages:
    161
    Likes Received:
    0
    Elero we dont wire blinds that unlike most jobs we fix up. Ill dig up a drawing I have later.We wire them basically to have one relay for the up and a second relay for the down and the 4 ch interlocking relay will only do two blinds. Power comes into common r1 then out NC r1 to common of R2 so only power will be able to reach one leg of the motor at a time be the mechanical interlocking. We use delays by various logic so there is less chance up a user selcting up then down etc. Is still think these relays have been getting worse of late.
     
    Nathan, Aug 7, 2007
    #7
  8. conor1

    conor1

    Joined:
    Feb 13, 2007
    Messages:
    135
    Likes Received:
    0
    Location:
    Northern Ireland
    hi markus ,yes thats the problem ,i thought this unit was a change over relay thus only supplying power to either n/o or n/c not both at the same time i read a thread regarding adding add capacitors ,as i have all channels used on relay.
    many thanks to all conor
     
    conor1, Aug 7, 2007
    #8
  9. conor1

    eleroAustralia

    Joined:
    Nov 12, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Germany
    Nathan: All done right

    You are right:
    The way you describe it, there should be no problems for the motors.
    The only thing that could still mess up something would be parallel wiring and the delay time maybe not working reliably in all cases (Timer event moving blinds, user overriding in opposite direction, delay time is still active?)

    But Clipsal actually described something in a whitepaper here which should resolve your problem:
    http://www.cbusforums.com/forums/showthread.php?t=3276

    ---------- Edited from here: added later on ----------

    I have gotten now the "All clear" from the Development Manager from elero GmbH (HQ in Germany) that it is o.k. to have our motors connected as it is described in the whitepaper on http://www.cbusforums.com/forums/showthread.php?t=3276 and that it will not affect the warranty.
    Some installers may like that piece of mind :D
     
    Last edited by a moderator: Aug 9, 2007
    eleroAustralia, Aug 8, 2007
    #9
  10. conor1

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    This will all be a mute point shortly when the new blind relays are released. Just wish they would hurry up as a customer put in some more roller shutters the other day and we want to use the new relay as soon as it is released instead of using the elero reg 2way (sorry eleroAustralia) and spare relay outputs.

    nathan - are you and conor1 working together - the original post seems to have gone to replying to you. I am still unsure from reading if conor1 has wired them up the way you have.

    Mick
     
    znelbok, Aug 8, 2007
    #10
  11. conor1

    eleroAustralia

    Joined:
    Nov 12, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Germany
    New C-Bus motor relay

    I am looking forward for the new C-Bus motor relay.
    I am going to/ getting calls from too many sites with messed up motors because of wrong wiring/ programming etc!
    If an installer in future doesn't use the C-Bus motor relay or another approved method, I have an simple answer for them in the future.

    Does anybody know how it is priced?
    Technical specifications? (Switching capacity under inductive load?)
    Can it also be used for Venetian blinds (Latching only after 1 or 2 seconds to adjust the slats)?
     
    Last edited by a moderator: Aug 9, 2007
    eleroAustralia, Aug 9, 2007
    #11
  12. conor1

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    There's a limit to how much we can say about unreleased products.

    What I can tell you :

    The price is listed in the latest Trade Product Guide.

    The unit has active and neutral input, with switched neutral, up, and down outputs.

    There is hardware interlocking to ensure up and down outputs cannot be powered simultaneously, and firmware interlocking to enforce a minimum 0.5s delay between up and down (and vice versa).

    The changeover delay and timeout period are configurable via Toolkit.

    I'm not personally familiar with the requirements for venetian blind control - can you elaborate on how this works and what is required?

    Nick
     
    NickD, Aug 9, 2007
    #12
  13. conor1

    eleroAustralia

    Joined:
    Nov 12, 2004
    Messages:
    44
    Likes Received:
    0
    Location:
    Germany
    Venetian Blind requirements

    For Venetian blind motors (as long they are AC) they have basically the same requirements as Tubular motors. They just are of different shape (square).

    The Blinds behave in the following way (95% of them in Australia, there are plenty more systems out in Europe):

    On running down the slats are closed.
    When the motor switched off on the bottom limit the slats are still closed.

    Driving the motor up will open the slats and drive the blind up.

    To get to any specific slat position/ adjust the slats to preferred position the user needs to be able to pulse the motor in any one direction.

    Usually this is achieved by the motor controller behaving:
    Button press of less than 2 seconds: Relay behaves like a momentary contact
    Button press of more than 2 seconds: Relay latches

    For user convinience most elero products also have a run-time memory:
    A double click will run down for a specific time (Running time of the blind from top to bottom limits, anything from 30 - 120 sec) and thereafter run the blind up for a specified time (usually just 0.5 -1.5 sec) to open the slats to the user preferred position.
    In this way the user doesn't need to wait around for the blinds to reach the bottom limit before he can adjust the slats.
    (I guess this can also be achieved by programming the saturn range of switches or other "logic" components on the C-Bus?)

    Is there any final release date available yet?
     
    eleroAustralia, Aug 9, 2007
    #13
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.