    I've just installed a CMU unit and it triggers the "remote on" on all of my output units. I've checked & changed c-bus cables, so it's not a cable fault. Could my CMU be faulty? Am I missing a vital configuration step somewhere?

    Any help would be much appreciated.
    Gaz.
     
    Beerygaz, Oct 28, 2012
    #1
  2. Beerygaz

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    458
    Likes Received:
    35
    Location:
    Sydney
    Sounds like a unit fault to me, most likely the infamous solder bridge :)

    I would send it back but you could make a 'Y' split cable and disconnect the Brown and Green pairs on the leg going to the CMU..

    J
     
    jboer, Oct 28, 2012
    #2
  3. Beerygaz

    Beerygaz

    Joined:
    Dec 25, 2005
    Messages:
    52
    Likes Received:
    0
    Location:
    Johannesburg, South Africa
    If it's just a solder bridge then I'm happy to cut the green & brown to the unit and put it on a dedicated leg. I was just worried it was something more serious. Toolkit can see the device on the network, so it seems everything else is working as expected. Thanks for the advice J.
     