CTC and MONO no sync

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by HSLee, Jan 7, 2009.

  1. HSLee

    HSLee

    Joined:
    Dec 16, 2008
    Messages:
    30
    Likes Received:
    0
    I was facing some problem that CTC and B&W no sync status.
    :confused::confused::confused::confused:

    Problem 1
    The system got 4 network (network A,B,C,D)
    CTC and B&W was in the same network A
    1) When using CTC to dim network B light , the status of B&W not according and remain the same percentage,
    but the status of DLT was according to the CTC.
    2) When using the B&W to dim network C light, the status of CTC and B&W is not according and remain the CTC was remain the same percentage
    ,but the status of DLT was according to the status of B&W

    We using PICED V4.4.0 and TK 1.9.3

    Problem 2
    Same problem with problem 1 but is Schedule Plus and the CTC , the status of either each part won't change accordingly.


    Problem 3
    Can i ask some question abotu C-Lution here?

    Hope expert member help me :)
     
    HSLee, Jan 7, 2009
    #1
  2. HSLee

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    If you use a unit on one network (A) to control a group on another network (B), other units on network A will not see the message.

    The easiest way around this is to have units on network A send the messages to network A and rely on "Application Connect" mode in the bridges to forward the messages for you. The other units on network A will then see the messages.

    Read the C-Bus Networks document for more details (C:\Clipsal\PICED\Manuals\C-Bus Networks.pdf).
     
    Darren, Jan 7, 2009