Curtain which use shutter relay for half open

Discussion in 'C-Bus Wired Hardware' started by damonfung, May 21, 2013.

  1. damonfung

    damonfung

    Joined:
    Apr 15, 2011
    Messages:
    11
    Likes Received:
    0
    Location:
    tuen mun
    Hello,

    I got the project that the customer requests to set the curtain in half open. However, I just know the shutter realy just can be programmed as fully open(255), fully close(0) and stop(5).

    How can I to make the curtain half open or 30% open or 70% open................?

    Thank you my buddy!
     
    damonfung, May 21, 2013
    #1
  2. damonfung

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,548
    Likes Received:
    178
    Location:
    Adelaide, Australia
    The Global tab of the shutter relay has an option that says 'Level Translation Mode'. If you check that the shutter will stop at the percentage open selected by the group address. You just can't select 1%, 2% 98% or 99% as these are still interpreted as the toggle commands. You need to set the fail safe delay to the exact time the curtain takes to open (plus a bit) as this is used to determine where to stop the curtain. Don't expect it to be exact, but it's good enough for most circumstances.
     
    Ashley, May 21, 2013
    #2
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.