    Hi
    I'm new to DALI and try to dim 20 T5 lamps via DALI
    I have a C-bus DALI gateway and OSRAM dim ballasts

    1. I don't have a tool to assign addresses to ballasts. Which is the easiest tool to do it?

    2. If i assign unit adress only, will it be enough to configure groups in ToolKit? Or i should decide what groups i need and assign it via DALI equipment

    3. Dali appears in Toolkit as an aplication. So need to choose it as a secondary application in keyswitch menu. But I can not use scenes for both lighting and dali applications in one switch simultaneously. Am I rigtht?
     
    Razor2204, Dec 10, 2011
    #1
  2. Razor2204

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,315
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    You will need to get hold of a Dali programming interface and software to program address into the ballast before connecting the CBus Dali interface.
    Tridonic have some interfaces and software but i cant tell you the latest versions.
    I have only one Dali installation but my thought would be that after assigning dali unit address to the ballast that you should also assign a dali group address based on areas you are likely to switch and can then map that to a single CBus group address.
    Once you have programmed all the ballasts and connected the CBus Dali interface then in Toolkit you can go to Dali interface and map Dali unit and group address to CBus group address.
    I used the lighting application for the Dali fittings.
     
    Last edited by a moderator: Dec 11, 2011
    DarylMc, Dec 11, 2011
    #2
  3. Razor2204

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,315
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    For the moment you will most likely find that if you drop the power to the Dali power supplies that all the lamps will come on.
    This may be of some use to you until you have the equipment to program the ballasts.
     
    DarylMc, Dec 11, 2011
    #3
  4. Razor2204

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,315
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    To Clipsal
    I don't know if it is possible but if the standard CBus Dali interface were able to be used with some software to program Dali ballasts I think it would be a great feature.
     
    DarylMc, Dec 11, 2011
    #4
  5. Razor2204

    Matthew

    Joined:
    Oct 26, 2007
    Messages:
    260
    Likes Received:
    1
    Location:
    Adelaide
    dimming new lamps

    Hi Razor
    Don't forget to run your new T5 lamps at Full Output (not dimmed) for the 1st 100hours. If you do not do this, they will fail early.
     
    Matthew, Dec 11, 2011
    #5
  6. Razor2204

    Razor2204

    Joined:
    Sep 18, 2010
    Messages:
    15
    Likes Received:
    0
    Location:
    Russian Federation
    What will fail laps or ballasts.
    I have a dsi tridonic ballast installed

    one lamp failed after some time
    changing the lamp didn't solve the problem.
     
    Razor2204, Dec 11, 2011
    #6
  7. Razor2204

    Colin1142

    Joined:
    May 2, 2009
    Messages:
    19
    Likes Received:
    0
    Location:
    Uk
    Dali ballasts used to have a dreadful failure rate, sometimes up to 20% (we have had tridonic out on a couple of occasions changing all balasts on a job! however the last one we did probably about 600 balasts we have only had about 5 failures in 6 months. We are desperate for the Dali gateway to be able to communicate the Em-pro status back to something like Schedule Plus as nearly every tender document we see asks for fully automatic emergency lighting with status reports. Tridonic software is our programming software of choice for the Dali side. We also find it easier to group the Dali ballasts in the Dali software rather than in the clipsal side.
     
    Colin1142, Dec 11, 2011
    #7
  8. Razor2204

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Fluoro lamps that are dimmed MUST be "seasoned" before they are dimmed. If you do not do this, the lamps will fail very early in their life.

    The seasoning process is to simply run the lamps at full brightness for 100 hours. Do this and they will last their rated lifetime.

    The 100 hours does not have to be all in one continuous go. You can do 8 hours / day for however many days until you have accumulated 100 hours. Just don't dim the lamps in the first 100 hours of operation.
     
    ashleigh, Dec 11, 2011
    #8
  9. Razor2204

    samluo

    Joined:
    Nov 3, 2009
    Messages:
    65
    Likes Received:
    0
    Location:
    SHENZHEN
    its easy to manage the address, groups and scenes even the clipsal gateway can not support directly.
    You can get a toolkit from Tridonic or Osram/Siemens to program the DALI ballasts.
    I have free DALI software to do that too.
     
    samluo, Dec 23, 2011
    #9
  10. Razor2204

    Razor2204

    Joined:
    Sep 18, 2010
    Messages:
    15
    Likes Received:
    0
    Location:
    Russian Federation
    the problem is that you can not control dali and cbus scenes from one c-bus switch.
     
    Razor2204, Dec 23, 2011
    #10
  11. Razor2204

    Razor2204

    Joined:
    Sep 18, 2010
    Messages:
    15
    Likes Received:
    0
    Location:
    Russian Federation
    Finally
    I assigned LIGHTINING as a main aplication for DALI module
    everything works OK, even scenes

    But there is one more question

    After I select a scene to turn off lightning
    the halogen lamps ramp to OFF
    and dali lamps INSTANTLY TURN OFF

    Is it possible for lumniscent DALI lamps to fade out
     
    Razor2204, May 21, 2012
    #11
  12. Razor2204

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,315
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    Hi Razor
    You should check the scene component.
    I have no trouble ramping the DALI fittings off from a scene.
     
    DarylMc, May 21, 2012
    #12
  13. Razor2204

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    458
    Likes Received:
    35
    Location:
    Sydney
    Also check that you have 'Match Ramp Rates from C-Bus to DALI' boxes ticked in the Map tab in the config of the DALI gateway.
     
    jboer, May 21, 2012
    #13
  14. Razor2204

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    DALI ballasts have their own internal rate of dimming. When C-Bus sends a level and a rate to DALI the rate is ignored.

    As DarylMc says, you need to turn on the 'Match Ramp Rates from C-Bus to DALI' option in the DALI gateway to override this behaviour of the ballasts.
     
    Newman, May 22, 2012