Dimmers on 3 phases

Discussion in 'C-Bus Wired Hardware' started by Dave Byron, Apr 15, 2005.

  1. Dave Byron

    Dave Byron

    Joined:
    Aug 3, 2004
    Messages:
    835
    Likes Received:
    0
    Location:
    Casurina
    Need a refresh on the connection of dimmers over 3 phase power supply, there is some smallprint so they dim correctly.

    dave
     
    Dave Byron, Apr 15, 2005
    #1
  2. Dave Byron

    Phil.H

    Joined:
    Jul 29, 2004
    Messages:
    466
    Likes Received:
    0
    Location:
    Sydney
    Dimmers and phases

    Dave,

    Guess you are referring to standard dimmers (din) and not high powered unit.
    For din ensure the phase of the power supply into the C-Bus section of the dimmer is the same phase as that supplied to the internal circuitry of the dimmer (right connections). The power connections do not have to be on the same circuit (circuit breaker -CB) however they do have to be on the same phase.
    A real good idea is to have each dimmer on its own CB, handy for isolating a unit when working on the associated load circuits etc
     
    Phil.H, Apr 16, 2005
    #2
  3. Dave Byron

    Dave Byron

    Joined:
    Aug 3, 2004
    Messages:
    835
    Likes Received:
    0
    Location:
    Casurina
    Phil

    Phil.H
    Thats it, tks for reminder

    dave
     
    Dave Byron, Apr 17, 2005
    #3