E5504DLWE - Unable to display label on secondary application

Discussion in 'C-Bus Wired Hardware' started by 2SC, Dec 16, 2012.

  1. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    We upgraded an old installation several weeks ago and among other things we installed 3 E5504DLWE instead of the old 5034N switches.
    Everything run smoothly except one thing that I would like to report:
    In the 8th button instead of the label we programed the 3 switches were displayed "8Button"
    The 8th button was the only one that used the secondary application that was actually the trigger application.
    Once I moved the G.A. to Lighting application (primary application), the E5504DLWE displayed the label as it was programmed...
     
    2SC, Dec 16, 2012
    #1
  2. 2SC

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    I think labels on the trigger application are only applied to scene keys.

    I'm guessing you're trying to do an On/Offf scene by using trigger on the secondary application. The only way I can think to get a label for such a scene is either to use a lighting application to trigger it, or use some logic to map alighting group to the correct trigger group/action selector(s).

    Nick
     
    NickD, Dec 16, 2012
    #2