Edlt Error loading config after refresh

Discussion in 'C-Bus Toolkit and C-Gate Software' started by Charlie Crackle, Jan 14, 2014.

  1. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    If you add a EDLT to existing network and then do a CTRL F5 (scan for new units)

    the new unit is found at 255. you can can then readdress or leave at this address. If you then double click the unit on the network to load the config from the unit. It loads to 85% and then says "Failed to load Unit"

    you can try again and again at it always fails at 85%

    =========================

    If you add a EDLT to existing network and then do a RESCAN entire network then device is found and you can edit it it fine.



    Is this a BUG ??

    having to do a rescan take along time. don't have this issue with other unit types

    Using toolkit 1.13

    Charles
     

    Attached Files:

    Charlie Crackle, Jan 14, 2014
    #1
  2. Charlie Crackle

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    Thanks for the report. We may need the Toolkit .ccl / C-Gate level 9 logs to diagnose this. If you do have them can you please zip and liam-e them to [email protected]?
     
    daniel, Jan 14, 2014
    #2
  3. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Have you tried to replicate using the steps explained ? Could it be this network? If it works ok for you I will spend the time to get the logs you require.
     
    Charlie Crackle, Jan 17, 2014
    #3
  4. Charlie Crackle

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    No worries, I've logged a ticket and we'll try to reproduce it.

    Ref: TK-9958.
     
    daniel, Jan 20, 2014
    #4
  5. Charlie Crackle

    chromus

    Joined:
    Jan 27, 2014
    Messages:
    422
    Likes Received:
    50
    Location:
    Perth
    Are the EDLTs loaded with the 1.20 firmware, this is the point at which mine give the warning when they aren't updated yet, so I assume it is the point when the version check is performed.

    Each unit gives the warning at 85ish %, once the update to 1.20 is done the warning goes away.
     
    chromus, Jan 30, 2014
    #5
  6. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Yes mind are version 1.2 firmware
     
    Charlie Crackle, Jan 30, 2014
    #6
  7. Charlie Crackle

    Robbo_VIC

    Joined:
    Jan 24, 2011
    Messages:
    143
    Likes Received:
    0
    Location:
    Melbourne, VIC
    I'm getting the same error when trying to open an eDLT which is already on the network and has been programmed before. Doing a Projects refresh or a Network Rescan doesn't fix it.
     
    Robbo_VIC, Jan 31, 2014
    #7
  8. Charlie Crackle

    Mr Mark

    Joined:
    Jan 27, 2006
    Messages:
    323
    Likes Received:
    5
    Location:
    FNQ
    I'm seeing this with eDLT firmware 1.3, anyone else still having trouble?
    I found opening from the database is a workaround.

    C-Gate runs on a RPi with no other clients connected while programming.
    Toolkit version is 1.13.3.
     
    Mr Mark, Jul 24, 2014