errors on first time toolkit programming

Discussion in 'C-Bus Toolkit and C-Gate Software' started by 71monaro, Apr 24, 2011.

  1. 71monaro

    71monaro

    Joined:
    Aug 6, 2010
    Messages:
    81
    Likes Received:
    1
    Location:
    Adelaide
    Sorry for being a newbie, but this is first time attempt at connecting toolkit to some hardware. I had entered into toolkit all my units for first project. I have wired up a PCI, universal 4channel dimmer and single input switch Key1.
    I placed the dimmer at address 001, with clock and software network burden enabled.

    When scanning the network Tool kit says it located 4 units. Three as expected plus a unit type 'Error failed to scan unit' at address 009.
    Then says unit address conflict at 009, and it tried, but failed, to unravell this unit.

    I then tried to edit Key1 so it operated channel one of this dimmer, but after editting toolkit to transfer to the network it said it failed.

    Am I missing anything.
    [​IMG][/url][/IMG]

    Does this give clue as to what I am doing wrong?
     
    Last edited by a moderator: Apr 24, 2011
    71monaro, Apr 24, 2011
    #1
  2. 71monaro

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    2SC, Apr 24, 2011
    #2
  3. 71monaro

    71monaro

    Joined:
    Aug 6, 2010
    Messages:
    81
    Likes Received:
    1
    Location:
    Adelaide
    There wasn't a physical burden in with the PCI. My understanding is I can use a software enabled burden? Is this insufficient for such a small test network?
     
    71monaro, Apr 25, 2011
    #3
  4. 71monaro

    71monaro

    Joined:
    Aug 6, 2010
    Messages:
    81
    Likes Received:
    1
    Location:
    Adelaide
    Still at a loss to get this simple network happening, (now 2 switches+dimmer+PCI.)

    It scans, and says it found either 5 or 6 units,
    Says error 7092, units with duplicate addresses found
    I try to resolve and it fails to unravell error 3772
    then retrieves unit info and lists the 4 units + extra item/s of unit type: 'failed to scan unit'

    I am also getting 'unit type only - serial mismatch' on the switches under column Exists in Database

    And I am unable to transfer programming to the network as i get error 45127, transfer of programming information failed.

    the network current consumption is 368mA, Supply 800mA,impedance 767ohms, but i think this is calculated from units, not a real reading.

    If I ping the network requesting network voltage, I get 32.5V and 32.1V for the dimmer and PCI, but 0.5V for the switches. Is this normal? Also each time I ping I either get the correct 4 units or incorrectly 4+1 or 4+2 units where the extra unit type is 'unknown' rescan.


    Stuck!
     
    71monaro, Apr 26, 2011
    #4
  5. 71monaro

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,315
    Likes Received:
    49
    Location:
    Cleveland, QLD, Australia
    DarylMc, Apr 26, 2011
    #5
  6. 71monaro

    71monaro

    Joined:
    Aug 6, 2010
    Messages:
    81
    Likes Received:
    1
    Location:
    Adelaide
    Thank you for that, I was able to the pre enable a software burden. All works, again thank you.
     
    71monaro, May 19, 2011
    #6