Flashing Indicator On Reflection Kp

Discussion in 'C-Bus Wired Hardware' started by audiovis, Mar 13, 2008.

  1. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    The system comprises
    18 x 8 gang reflection keypads
    12 x 4 gang relection keypads
    2 x colour touch panels
    3 x 5508D1A 8ch x 1A dimmers
    4 x 5512RVF 12ch x 10 Voltage Free Relays
    4 x 5508DSI 8ch DSI Fluorescent dimmers
    2 x 5104D5 4ch x 5A Pro Dimmers
    2 x 5102RVF 2ch Volt Free relays
    5 x 5504D2A 5ch x 2A dimmers

    In the case of the dimmers I have dimply assigned the group address to a switch and defined the switch as "dimmer".

    Press and hold causes the circuit to brighten/ dim
    Momemtary press & release causes the circuit to switch on BUT the indicator starts to flash at about 4 Hz for a LOOONG time, during which time pressing the switch DOES ABSOLUTELY NOTHING! Eventually after it stops flashing you can touch the switch and the circuit switches off - BUT The indicator starts flashing again.

    At any time, whilst the indicator is flashing, press and hold will stop the flashing and control the circuit as it should.

    The global settings are standard (Debounce, long press, etc)
    Key functions are also standard (Idle, Toggle, downcycle, end ramp)
    Block settings show 0h0m0s on the timer - it is not a timer issue as the LED flashes much faster.

    I suspect a network related problem but as it is a big install I am not sure where to start.
     
    audiovis, Mar 13, 2008
    #1
  2. audiovis

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Does it only do this on one keypad? if so, what happens if you swap it with another (in a different position on the network)?

    Do you have enough power supply (check voltage) and you probabbly won't need a burson on such a large network

    cheers
     
    Conformist, Mar 13, 2008
    #2
  3. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    Keypads

    No - it happens on ALL the keypads

    I did forget to mention I also have a 5500PC PC Interface on address 001 with both clock and burden activated.

    When I click (in Toolkit) on network it reports 1 burden required

    Current required = 714mA
    Current supply = 3320mA
    Impedance = 1418 Ohms
    52 Units

    Yes - for this project I did not want to mess around so anything that could include a power supply I ordered with power supply.
     
    audiovis, Mar 13, 2008
    #3
  4. audiovis

    PSC

    Joined:
    Aug 3, 2004
    Messages:
    626
    Likes Received:
    0
    Location:
    Brisbane, Australia
    Audiovis,

    You have a MASSIVE over supply of power!

    You could remove 13 powered output units and still have enough power for your network and save your client $1300.

    The first thing I would be doing is reduce the number of powered output units to about 6 and retest your network then.

    If the network is stable try adding the output units back in one at a time.
     
    PSC, Mar 13, 2008
    #4
  5. audiovis

    PSC

    Joined:
    Aug 3, 2004
    Messages:
    626
    Likes Received:
    0
    Location:
    Brisbane, Australia
    Try using the C-Bus calculator next time before ordering, it may save you some time and money...

    Just remember that the network information (power, burden etc) that Toolkit is displaying is not being read from the network, it is purely a calculation within Toolkit based on the units in your project database.
     
    PSC, Mar 13, 2008
    #5
  6. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    Have just returned from site - Calculated the total power supply is 2120mA.

    Diconnected 3 relay units - each with 200mA, reapplied power and problem still there.

    I had only one device clock enabled so I enabled 2 more (three in total) and problem seemed to go away - even with the three 12 way relays reconnected. Packed up and did last check and - problem back again.

    Re-connecetd and, on a whim, enabled another burden on the upstairs touch panel - Problem gone!!???

    Waited about an hour on site going from panel to panel - problem seems to have gone away!??

    One point - the site is pretty extensive and most of the C-Bus wiring is "star" topology so we are pushing the 1000m cable limit.

    We do intend to exchange two or three units for units without power supply. However, on a house costing in excess of AUS $2,000,000 - a few thousand was less relevant than getting the system in and working. Will use the calculator in future though.
     
    audiovis, Mar 13, 2008
    #6
  7. audiovis

    PSC

    Joined:
    Aug 3, 2004
    Messages:
    626
    Likes Received:
    0
    Location:
    Brisbane, Australia
    With that much cable the need for burdens would be reduced.
     
    PSC, Mar 13, 2008
    #7
  8. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    This is what I (and the local Clipsal Importers) thought - yet - with only one burden enabled the flashing problem comes back! As soon as we enable two burdens the problem appears to resolve itself (Although I am unconvinced!)
     
    audiovis, Mar 13, 2008
    #8
  9. audiovis

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Charlie Crackle, Mar 13, 2008
    #9
  10. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    Thank you. It also explains how multiple power supplies can be connected together.

    I will be reducing total supply from 2120mA to 1520mA during next week.

    Is the concensus that this is why I had a flashing indicator though? It was still flashing after I had shed 1,2A of power supply but, granted, before I had enabled additional clocks and the second burden.
     
    audiovis, Mar 13, 2008
    #10
  11. audiovis

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Flashing indicators on key units when you press a key as you describe indicates that the unit was unable to communicate on the network.

    It sounds like you are on track to solving it, but I'd be implementing all of the suggestions re getting your network withing spec (cable length, power supply limits).

    This feature is in any key unit with firmware later than 1.5.0 (it was also in version 1.0, but was removed in 1.2.67 through 1.5.0).

    Nick
     
    NickD, Mar 13, 2008
    #11
  12. audiovis

    audiovis

    Joined:
    Nov 24, 2006
    Messages:
    9
    Likes Received:
    1
    Dear Nick/ Peter/ Charles

    Thank you all - your input has been very useful. I will, in future be a little less blase when it comes to the bus wiring and the power supplies needed.

    I must admit, however, that I have no real confidence, as yet, that the problem on this particular project is nailed.

    Regds
    Richard
     
    audiovis, Mar 14, 2008