Flourescent Dimming

Discussion in 'C-Bus Wired Hardware' started by rodime, Jan 4, 2006.

  1. rodime

    rodime

    Joined:
    Jan 4, 2006
    Messages:
    1
    Likes Received:
    0
    I am needing to dim 2x58W flourescent lamps that use a Tridonic PCA dimming balast. Can anyone advise which Clipsal Cbus dimmer unit would be capable of achieving this?
     
    rodime, Jan 4, 2006
    #1
  2. rodime

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,429
    Likes Received:
    64
    Location:
    Adelaide
    There are quite a few different "Tridonic PCA" ballasts. They support one or more types of control input, 0-10V, DSI, or DALI. I assume you have them at hand, so you can probably check.. most of the ones I've seen are marked pretty comprehensively on the ballast itself.

    If they have a 0-10V control input, you can use an analogue output unit (L5504AMP).. this is fine for a few ballasts on short runs.

    DSI and DALI are two different digital control methods, each with its own strengths and weaknesses. CIS have gateways for both DSI and DALI (we don't call them dimmers, because they're not actually doing the dimming) :

    DSI gateway : L5508DSI or L5508DSIP
    DALI gateway : 5502DAL

    I suspect if you only have a few ballasts to do, the analogue output will be the simplest/cheapest option (if the ballasts support it). If you have to/want to go the digital route, the DSI will be the easiest way to go, as it doesn't require any special commissioning tools (as DALI does), and the cost of these and your time will outweigh the slightly higher price of the DSI gateway over the DALI gasteway.

    HTH,

    Nick
     
    NickD, Jan 4, 2006
    #2
  3. rodime

    marka

    Joined:
    Aug 5, 2004
    Messages:
    24
    Likes Received:
    0
    fluro dimming

    go with the clipsal dsi
    quick and simple and will save you a lot of headaches
     
    marka, Jan 5, 2006
    #3
  4. rodime

    JohnC

    Joined:
    Apr 6, 2005
    Messages:
    554
    Likes Received:
    1
    Location:
    Sydney
    If it's only a small installation, I'd investigate the cost to replace the ballasts with Analogue (0-10V controllable) then use the 5101R - that unit has a current-sinking 0-10V analogue output in it (although not well documented). It may be that the cost of changing the ballast will be cheaper than buying a Gateway!

    For a larger install, or where you don't have a say in the ballasts, then you have to use whatever gateway / interface is required by the ballasts. In the case of Tridonic, they always try to push "their own" DSI interface, rather than the more widely used DALI - it's the way that they hold specification on projects because nobody else really supports DSI.

    Cheers, JC

    PS: As Nick said, none of the fluorescent ballasts are "dimmable" - they need a control signal of some form to regulate their light output.
     
    JohnC, Jan 16, 2006
    #4
  5. rodime

    Mr. Mark

    Joined:
    Nov 12, 2004
    Messages:
    3
    Likes Received:
    0
    JohnC,
    Do you have any documentation on this feature of the 5101R ?
    We have a need for something like this coming up soon.

    Thanks,

    Mark
     
    Mr. Mark, Jan 18, 2006
    #5
  6. rodime

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Newman, Jan 18, 2006
    #6
  7. rodime

    JohnC

    Joined:
    Apr 6, 2005
    Messages:
    554
    Likes Received:
    1
    Location:
    Sydney
    One annoying thing about that device - unlike other output devices that can draw operating power for C-bus via the Cbus cables, this one is completely self-powered so it acts very wierdly unless connected to the mains. Well, actually, it doesn't do anything AT ALL unless connected to the mains.

    Make sure to note the comments in that document about the programming switch - I nearly went crazy with these devices because unless that button is held down they won't even show up in a scan, let alone allow programming !

    But they work quite nicely, and they will work with more than 2 ballasts given a bit of fiddling and good luck.

    Cheers, JC

    PS: These units were designed specifically to be mounted inside a luminaire - they allow individual control that is safe and legal (the relay) at an affordable price. The idea is not to bring all the loads back to a switchboard - it's true distributed control. It's a device I was involved in developing a very long time ago, but unfortunately everyone has gone crazy for the "stick all the Cbus in a cupboard and run 3 miles of cables out to every load" concept now days... :)
     
    Last edited by a moderator: Jan 19, 2006