General Input module?

Discussion in 'C-Bus Wired Hardware' started by daky, Nov 13, 2009.

  1. daky

    daky

    Joined:
    Oct 30, 2009
    Messages:
    21
    Likes Received:
    0
    Location:
    home
    Whenever Toolkit scans the General input module it always takes a great deal to time and on several occasions communication during scan stops?

    Is this common for this type of modules because it has a lot of configuration and setup windows?
     
    daky, Nov 13, 2009
    #1
  2. daky

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Uploading or downloading parameters with this unit takes a lot longer than it does for most other C-Bus units. This is because this unit has a lot more configuration parameters than something like a DIN dimmer or relay.

    If the communication is actually failing then it suggests that the network may have some communication problems. I suggest you run the C-Bus Diagnostic utility on your network. Run the traffic analyser and look for communication errors.
     
    Newman, Nov 13, 2009
    #2
  3. daky

    Memphix

    Joined:
    Aug 31, 2006
    Messages:
    248
    Likes Received:
    1
    Location:
    Australia
    Failing could be due to burden settings. Ensure you have the correct number of burdens on the network (includes both software and hardware burdens).

    Not sure if there is a difference, but I prefer using hardware burdens where possible.

    If that still doesn't work, try adding one more burden than the recommended etc.
     
    Memphix, Nov 16, 2009