Hi folks. I'm having an issue gaining stable sensor readings using a General Input Module, and hope someone may have a suggested fix. The issue is a wandering reading for each sensor, which equates to an unscaled fluctuation of between 1-7 out of 255 level, or up to 3%, with the reading changing in this range at every "Show Current Level" sample (in Toolkit). When scaled, this makes the temperature readings bounce around by +/- 1 degree Celcius. The sensors and associated gear are high quality, and of differing types, which indicates the sensors are likely not the issue. I have four sensors currently connected: - Pt100 via Delta Ohm HD988TR1 temperature transmitter (4-20ma), calibrated 0-50C - Pt100 via Delta Ohm HD988TR1 temperature transmitter (4-20ma), calibrated 0-50C - Viasala Humitter 50Y temperature transmitter (0-1V) - Viasala Humitter 50Y humidity transmitter (0-1V) Input power is 24VAC. Tried both DIN rail PSU and the Clipsal supplied PSU to isolate that, and no change. A digital volt meter reads the 0-1V sensors stable at 1/100 of one volt, so no fluctuation there. I have not put a meter on the 4-20ma sensor transmitters as yet, but am not expecting fluctuation given the newness and quality of the kit (and there are two of them that give the same result). The fluctuations have also been consistent over a one week period so far, and occur whether shortly after the unit is powered or after many days of operation. I have not tried a regulated input voltage to the unit or sensors as yet, as it didn't seem worth it given my DVM readings of 0-1V sensors not moving and accuracy rating of the 4-20ma transmitters with respect to voltage fluctuation (0.4uA/V, with transmitter resolution of 4uA). Any ideas? Steve.