General Input Unit and Water Tank Sensors

Discussion in 'C-Bus Wired Hardware' started by leeandj, Dec 12, 2011.

  1. leeandj

    leeandj

    Joined:
    Apr 13, 2006
    Messages:
    39
    Likes Received:
    0
    Location:
    Park City, UT
    After reading this thread, we purchased two Anadex sensors and a GIU.

    I have configured them according to the instructions, but am confused as to the output results.

    The sensors operate between 0 and 4m depth, and output 4 - 20mA. My tanks are full (at 1.8m depth), and the sensors output 11.83 mA at this depth.

    I am sure that the multiplier and offset are correct as inputting these values into the format y=mx + b yields the volume in litres that I would expect.

    Questions are as follows:
    1. Why does the Current Level show 40%? What does this correspond to? What does the value '246833' mean?

    2. The values broadcast on the measurement application seem bizarre! How can I have negative numbers?

    Any help much appreciated,
    Lee& J.
     

    Attached Files:

    leeandj, Dec 12, 2011
    #1
  2. leeandj

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    1.8m is 45% of 4m. This is probably where the 40% figure comes from (with some error).

    2544 x 40/100 * 255 - 10178 = 249,310 so the figure of 246,833 is roughly correct.

    It is not clear why the Measurement Application Manager in PICED is showing negative values. Use the C-Bus Diagnostic Utility to look at the messages on C-Bus to see what is being broadcast.
     
    Darren, Dec 13, 2011
    #2
  3. leeandj

    simont

    Joined:
    Jul 14, 2009
    Messages:
    11
    Likes Received:
    0
    Location:
    Herne Hill
    Lee,

    Not sure if you still have an issue with the GIU and Anadex sensors. I have used them before for customers and have had an issue with the online calculator from Anadex.

    The sensor has a range of 0 to 4.5 m, so 1.8 / 4.5 = 40%. This part is correct.

    I use a different formula for the multiplier and offset though. Use the same values for your Depth when the tank is full and for the Capacity, but try the following and put the multiplier into Toolkit. Make sure the Units Of Measurement are correct and tick Show Current Level.

    Multiplier = (4.5 * Capacity) / (255 * Depth)
    Offset = 0


    Simon.
     
    simont, Jul 2, 2012
    #3
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.