Intermittent All On

Discussion in 'C-Bus Wired Hardware' started by Elliott L, May 1, 2024.

  1. Elliott L

    Elliott L

    Joined:
    Oct 7, 2020
    Messages:
    3
    Likes Received:
    0
    I have a customer with a very basic system consisting of dimmers, relays, key inputs and a few sensors. No screen, wiser, PAC, no scene control.
    Every so often, fortnightly maybe, everything turns on. Usually at night. Everything can be turned off but you need to walk around the entire home to do this.
    I thought it could be a comms wiring issue but this has been fully checked. Haven't been able to check the log as it never happens when I'm on site.

    Any thoughts?
     
    Elliott L, May 1, 2024
    #1
  2. Elliott L

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,667
    Likes Received:
    226
    Location:
    Adelaide, Australia
    This is most likely caused but leakage across the remote on connections somewhere in the cabling. Any sort of contamination from water or rodents etc can cause this. Neither the remote on or remote off pairs are ever needed in a domestic install but they are often connected through anyway. You could check each termination individually, or if all output units are in a single enclosure, just try disconnecting the remote on/off pairs going into the enclusure.
     
    Ashley, May 2, 2024
    #2
  3. Elliott L

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    If it were the remote on connection then you wouldn't be able to turn the loads off again by walking around the house.

    It could be the power recovery behaviour being triggered by noise or a power glitch or as a result of a power supply failing.

    A simple way to check if this is what's happening is to change the power recovery settings to all restore to off. If the loads now all turn off occasionally then that's what's going on.
     
    NickD, May 10, 2024