IO device with hour meter

Discussion in 'C-Bus Wired Hardware' started by dave240t, Sep 25, 2009.

  1. dave240t

    dave240t

    Joined:
    Apr 10, 2008
    Messages:
    26
    Likes Received:
    0
    Does any one know of a electrical hour meter that can be connected into a general input module so that a touch screen could display hours on a lamp or is there a hour meter that uses serial that could be connected into a pac and then displayed??
     
    dave240t, Sep 25, 2009
    #1
  2. dave240t

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Schneider have a kW/h meter about the size of a circuit breaker that puts out 100 pulses per kW/h. You can feed the output into a bus-coupler or aux input unit. It's part no is EN-40. It can support a total load of 40A
     
    Conformist, Sep 26, 2009
    #2
  3. dave240t

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Are you talking about for a single load (lamp)?

    It is simple to use a current clamp with an analogue output for measuring power at the switchboard.
     
    Darren, Sep 26, 2009
    #3
  4. dave240t

    dave240t

    Joined:
    Apr 10, 2008
    Messages:
    26
    Likes Received:
    0
    i use cbus relays to drive contactors. I just want to read the hours of how long the cbus relays are on not
     
    dave240t, Oct 6, 2009
    #4
  5. dave240t

    dave240t

    Joined:
    Apr 10, 2008
    Messages:
    26
    Likes Received:
    0
    i have mesure hours using touch screens using logic but when pwr is reset the touch screens lose the hrs this is why i need a third party hour meter to count the hours
     
    dave240t, Oct 6, 2009
    #5
  6. dave240t

    Phil Summers

    Joined:
    Jun 26, 2009
    Messages:
    41
    Likes Received:
    0
    Location:
    UK
    I haven't played with User-defined SystemIO variables but the help files say that these "provide a means of non-volatile storage"
    Could you not count the pulses from Mr Conformist's Schneider kWh meter in a SystemIO variable (rather than a normal variable)?
     
    Phil Summers, Oct 6, 2009
    #6
  7. dave240t

    Damaxx

    Joined:
    May 12, 2008
    Messages:
    229
    Likes Received:
    47
    How would you program the input of this unit that conformist refers to onto a graph on homegate to display the current power usage of that load? logically using logic.. pardon the pun.... but I wouldnt know even where to start if someone could assit it would be greatly appreciated. I get this request all the time.
     
    Damaxx, Apr 15, 2010
    #7
  8. dave240t

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    You don't need to use logic. It is actually very simple:

    1. Use the Power Meter Manager to add your pulse power meters or analogue power meters

    Power Meter 1.JPG

    2. Place a graph component on a page

    Power Meter 2.JPG

    3. Set the graph component to display the value of the "Power Meter Total" in-built system IO

    Power Meter 3.JPG

    This should all take less than 5 minutes.
     
    Darren, Apr 15, 2010
    #8
  9. dave240t

    Damaxx

    Joined:
    May 12, 2008
    Messages:
    229
    Likes Received:
    47
    Thanks Darren. Had never seen the power meter manager in homegate.

    Will give it a go. Looks like a walk in the park.
     
    Last edited by a moderator: Apr 19, 2010
    Damaxx, Apr 19, 2010
    #9
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.