    Hi All,

    I'm building a deck at home, and looking into installing some deck lights.

    I would like to go with LEDs, and ideally RGB so I can change the colour under C-Bus control.

    Ideally I would like something :
    - that mounts within the width of a 90mm deck board*
    - made from stainless steel
    - waterproof
    - that is well made, but doesn't cost the earth

    Can anyone recommend any good suppliers? There are bucketloads on the net, but it's hard to know without buying a sample whether the quality is any good. It's also hard to find any wiring diagrams or even decent technical info.

    Cheers,

    Nick

    *flange less than about 80mm and cutout less than about 60mm
     
    Last edited by a moderator: Mar 13, 2012
    NickD, Mar 13, 2012
    #1
  2. NickD

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,425
    Likes Received:
    37
    Location:
    Adelaide, South Australia
    You want mounted down low? At foot height... under a hand rail? Or something else (I don't quite understand exactly where you want to put it).

    PM me... might know of a solution.
     
    ashleigh, Mar 13, 2012
    #2
  3. NickD

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Based on this
    - that mounts within the width of a 90mm deck board*
    I would say that it is mounted in the deck board pointing up. have seena lot of LED's for this.

    I think the challenge is being able to change the colour via C-bus. That solution alone is something I would like to know more about.

    I believe it can be done via DMX and maybe 0-10V outputs but I have not seen anyone talk about i there at all - especially wth respects to how they have set up the system (colour vs value and the logic used.)

    Mick
     
    znelbok, Mar 13, 2012
    #3
  4. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    Hi Mick,

    As far as I'm concerned, this is the easy bit :) I have a C-Bus DMX gateway in my box of samples. That coupled with a 3 channel LED driver with DMX input (which seem relatively easy to come by) and it's pretty straightforward. 0-10V is also an option, but a) I don't have one, and b) it's limited to 4 channels, whereas the DMX gateway does 12, so I can use the same gateway to do some effect lighting for the upcoming bathroom renovation :)

    In both of these cases, it's just mapping a group address to each of the R, G, and B levels to get whatever colour you want. You can have scenes with different combinations of R/G/B to get preset colours, and if you have a touchscreen or Architectural dimmer than can cross-fade scenes, you can blend between colours (if you don't have these you can just run slow ramps to the new values).

    Nick
     
    NickD, Mar 13, 2012
    #4
  5. NickD

    Ashley

    Joined:
    Dec 1, 2005
    Messages:
    1,667
    Likes Received:
    226
    Location:
    Adelaide, Australia
    I had the same issue when trying to control 12V RGB lights for my home theatre. After looking through the limited (and very expensive) commercial options I just built my own using an off the shelf PIC controller board, 4 output drivers, a CBus SIM module, PC power supply and a bit (well quite a lot actually) of software. It can control 32 12-24V leds circuits at 1 amp per circuit (which is a lot of leds!). The 8 bit CBus level is converted to a 16 bit PWM signal via a logarithmic lookup table to give nice even brightness control. It uses 64 group addresses (on a unique lighting application). The first 32 control the individual leds (or RGB if you hook up colour leds). The next 32 groups control the RGB groups using HSV (Hue, Saturation, Value) colour space which is a lot more convenient. There are also other groups which can cycle the Hue at different rate to give a nice colour changing effect. I keep on adding stuff as time permits :)

    If anyone is keen enough to assemble one I'm happy to share the code.
     

    Attached Files:

    Ashley, Mar 13, 2012
    #5
  6. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    Wow... nice work.

    It looks like fun... I used to do all sorts of stuff like this, but now I have 2 kids under 2 :)

    Nick
     
    NickD, Mar 13, 2012
    #6
  7. NickD

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    Unfortunately LED Lighting in Peakhurst are one of the best suppliers in this speciality. You will come to realise my comments if you question their god status.

    I also visited Victorian Eco Lighting when I was last in town.
     
    tobex, Mar 14, 2012
    #7
  8. NickD

    Matthew

    Joined:
    Oct 26, 2007
    Messages:
    260
    Likes Received:
    1
    Location:
    Adelaide
    What lights?

    Hi Nick
    Regarding the trend of little LED lights in the (Aussie institute) deck facing directly up, think about exactly what you are trying to achieve and then how you go about that.
    1) They can be very glare-y, as you walk over/past them, you don't want them in your usual line of sight.
    2) where will they light? you can't see light in air......they have to shine on something so you can see the light.
    So maybe,
    You put them in front of the posts/railing so they can highlight them. Similarly any steps, or changes in ground level are very good items to highlight.
    Not much point of shining them on a dark coloured transparent roofing.

    On value there are lots of cheap and economical options at bunnings. Digilin make the best one I've seen http://www.digilin.com.au/products.asp?name=Taipan Exterior 3W RGB LED Light, I think Moonlighting are distributing it, but haven't asked the price.

    Happy lighting.
    Matthew
     
    Matthew, Mar 15, 2012
    #8
  9. NickD

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,425
    Likes Received:
    37
    Location:
    Adelaide, South Australia
    Pretty much what I had in mind - a LED variation on the older weatherproof halogen uplighters that have been around for ever.

    You can also get a cable LED which is a roll-out strip, just nail or staple it to something like rails, under stairs, onto ballustrades and so on. Not sure exactly where to get it though.

    You might also consider these: http://pierlite.com/au/10740/inground
     
    Last edited by a moderator: Mar 16, 2012
    ashleigh, Mar 16, 2012
    #9
  10. NickD

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    Like I said ... LED Lighting has it in rolls. But I looked at the light output and it was mediocre. Good for soft lighting.
     
    tobex, Mar 16, 2012
    #10
  11. NickD

    daveymit

    Joined:
    Sep 25, 2012
    Messages:
    26
    Likes Received:
    0
    Location:
    Wollongong

    Hi Nick,
    I like your enthusiasm!! :). I am interested in this concept but have a question. You said you drive DMX output from the gateway to a driver with DMX capability, which then controls the RGB levels out to a load (LED rgb strip??). You then said that you can use the same gateway to control your new addition of a bathroom. Does that mean you will just add another DMX led Driver after the gateway (in parallel with the original driver), then run your bathroom lighting off that? Thus controlling two different rooms of lighting off the same gateway? If so, is there something in the software when you program the gateway to say - this group address will activate led driver #1 (for example), and another group address will activate led driver #2.??

    Or if you want to have individual control of rooms then you need a gateway for each room?

    Does this make sense? Sorry if i have confused you, let me know and i will try and clarify :).

    Cheers,
    Dave
     
    daveymit, Oct 21, 2012
    #11
  12. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    Hi Dave,

    Yep. Note that DMX uses RS485, running at 250kbps, so depending on the length of the run, the quality of the cable, and the environment, you may or may not need to worry about termination. If your runs are short, and you use a twisted pair, you probably don't need to worry about it.

    Yep. DMX has 512 channels (called "slots"). The C-Bus DMX gateway has 12 group addresses. In Toolkit, you configure the group to slot mapping. You then need to set the LED driver to the right slots.

    Nick
     
    NickD, Oct 22, 2012
    #12
  13. NickD

    daveymit

    Joined:
    Sep 25, 2012
    Messages:
    26
    Likes Received:
    0
    Location:
    Wollongong
    Hi Nick,
    Thanks for your prompt reply. Your information was very helpful. Just a few thoughts...

    What sort of length are we talking? I have read that DMX networks can have cable lengths up to 450m?? Also, what cable would you recommend for the DMX network? Would cat5e cable suffice? Runs would be, at guess, approximately no longer than 50m per Driver???

    Will the specific drivers i choose have selectable addresses? Which drivers do you use?

    Thanks again for the help!

    Dave
     
    daveymit, Oct 22, 2012
    #13
  14. NickD

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    459
    Likes Received:
    35
    Location:
    Sydney
    Like everything there is a standard for DMX and its install but basically if you are doing an install that is not going to get to disturbed you will be fine using Cat5e. I would really recommend using shielded cable though. DMX is reasonably forgiving because it broadcasts at such a fast rate and so missing a bit or two doesn't really matter but if you happen to run your unshielded cable next to a dimmed load you will probably know about it fairly quickly.
    Like Nick said you would probably be fine not terminating, but for the cost and effort of putting a 120 Ohm resistor in on the end of your line it can save you grief later...

    Depends on what you get, but generally all DMX equipment is addressable. The question is how easy :) the little white $5 boxes you get on 'Buy It Now' .com essentially need an EPROM flasher to address them that will cost you another hundred or so.
    Generally though most drivers will have DIP switches for setting the address in Binary, just investigate what you are buying. Also if you are going to be buying more expensive LED strip/fittings rather than just 3528 LEDS on a strip or the similar make sure they are compatible with the driver you are planning on getting. (ie. Constant Voltage or Constant Current ect)

    As with everything spend as much as you can on the driver, Cheap ones will have very bad dimming and won't be as nice to your LEDs.

    Depending on your budget and LEDs I can suggest a couple of drivers if you would like. However I would also be interested on the drivers Nick uses and how he has found them, as I am always on the lookout for other options!?
     
    Last edited by a moderator: Oct 22, 2012
    jboer, Oct 22, 2012
    #14
  15. NickD

    daveymit

    Joined:
    Sep 25, 2012
    Messages:
    26
    Likes Received:
    0
    Location:
    Wollongong
    Hello jboer,

    Thank you for your input ;).

    What do you and Nick mean by not 'terminating'. I am taking this literally, so the physical terminations of the DMX network??
    Is the 120 Ohm resistor installed due to the DMX network needing to see a given load? If so, shouldn't this be built in to the output of the gateway?


    I was looking at the 5050SMD led strips. There are kits you can purchase over eBay from the US that have a dmx driver and power supply included with the strip. Would these be ok? Here is an example:

    http://www.ebay.com/itm/sirs-e-LED-...age_Lighting_Single_Units&hash=item58970dde97

    Any suggestion would be great here. As i have no experience with the use of DMX, any suggestions are welcomed :).

    Once again, thank you for your input. Without these forums, it would be very difficult to get by.....
     
    daveymit, Oct 24, 2012
    #15
  16. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    I haven't actually installed them yet.. too many projects (two of which are daughters under 3.. which makes it difficult to push the go button on renovating the only bathroom with a bath!).

    I got a few quotes from places that I have been referred to as reputable suppliers, and found several were offering the same drivers.. Unfortunately the only versions they offered were constant voltage, and some of the fittings I was looking at required constant current, so they wanted to sell me a "repeater" to convert the output to constant voltage. Google lead me to the manufacturer, who I found did another version with a constant current output. I also found they were in Shenzhen, so I got a colleague to buy them
    directly from the manufacturer for about 1/10 of what I would have paid :)

    This is the constant voltage version :
    http://www.sunricher.com/dmx512/dmx512-decoder/dmx512-decoder-sr-2102b.html

    I couldn't find a link on that site for the constant current version, but it is SR-2112B, and google will find that for you elsewhere.

    Nick
     
    NickD, Oct 25, 2012
    #16
  17. NickD

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,468
    Likes Received:
    84
    Location:
    Adelaide
    Google RS485.. there should be heaps of stuff on it, but basically if you're terminating, you need to do it at the the far end of the line, which is why it's not built into the driver output.

    Nick
     
    NickD, Oct 25, 2012
    #17
  18. NickD

    jboer

    Joined:
    Apr 27, 2012
    Messages:
    459
    Likes Received:
    35
    Location:
    Sydney
    This kit is reasonable, those drivers are ok, but are on the cheaper side. The only thing is that if you are dimming at around 0-30% you can get some nice strobing effects :)

    As Nick said read the wiki on RS485 and DMX so that you can get the full picture. But apart from it needing to be on the end of the line for other reasons in some circumstances you don't want to permanently load your line.

    J
     
    jboer, Oct 25, 2012
    #18
  19. NickD

    daveymit

    Joined:
    Sep 25, 2012
    Messages:
    26
    Likes Received:
    0
    Location:
    Wollongong
    Thanks guys for the info. And thank you to Wiki ;). Where would we be without Wiki??

    I guess i will just have to trial the termination at the time of the install to see whether i need to terminate. Im thinking i will just use cat5e cable for the DMX network too. Any comments?


    Also, just a question regarding this forum, Is there a 'notification' option somewhere to notify me when there has been a reply on post that i was involved with? I am just getting a bit tired of going into my profile and looking at all of my recent threads and checking it manually.....

    Cheers
    Dave
     
    daveymit, Oct 28, 2012
    #19
  20. NickD

    DarylMc

    Joined:
    Mar 24, 2006
    Messages:
    1,340
    Likes Received:
    54
    Location:
    Cleveland, QLD, Australia
    Hi Dave

    I've not used a whole lot of forums but I reckon this one has excellent features.

    If you subscribe to a thread you should recieve email updates.

    User CP (control panel) has a lot of other settings.
     