LED's on mirror flashing

Discussion in 'C-Bus Wired Hardware' started by phcjpp, Aug 25, 2008.

  1. phcjpp

    phcjpp

    Joined:
    Oct 19, 2004
    Messages:
    112
    Likes Received:
    0
    Location:
    London
    Hi Guys,

    Just installed a mirror with LED's all around it. Its a simple 240v connection. I was replacing a simple light attached to a CBUS 1A dimmer. I assumed that I could only run the mirror at 0% or 100% (this is fine) but when at 0% the LED's pulse on and off! Weird. I imagine its something to do with residual current in the dimmers or similar ? Anything I can do to make this work other than buying a relay instead (real pain to do this) ?

    Thanks

    Chris
     
    phcjpp, Aug 25, 2008
    #1
  2. phcjpp

    amberelectrics

    Joined:
    Aug 29, 2007
    Messages:
    114
    Likes Received:
    0
    You can't run the LED's on a dimmer. You will need a relay.

    Think its because the dimmers sink some current through the circuit at all times. This makes the LED's turn on.
     
    amberelectrics, Aug 25, 2008
    #2
  3. phcjpp

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Do a search on the forum for Dimmer Leakage Current. A similar issue exists when some compact fluorescent lamps are connected to dimmer channels.

    If you want Off to be genuinely Off you'll need to use a relay.

    If you're having trouble fitting/wiring a DIN Relay unit into the job try a 5101R or 5102RVF instead.
     
    Newman, Aug 26, 2008
    #3
  4. phcjpp

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    If you could get a processor controlled filter then you could arrange it so that the load would drop out once the dimmer reached a certain level.

    The cost of such a technology would run into the dollars (four or five) and could happily sit on the driver circuit of the LED drivers. But sadly, due to the dire state of manufacture these simple things get let out for profit.

    I remember speaking to one of the largest LED suppliers in Australia and they made millions of excuses why they shouldnt sell LED's to the public and how you needed a PCB for the drivers .... once I told them I could have a prototype running in 6 days they decided to front up and tell me they didnt sell to the public.
     
    tobex, Aug 26, 2008
    #4
  5. phcjpp

    ICS-GS

    Joined:
    Nov 1, 2004
    Messages:
    347
    Likes Received:
    0
    Location:
    SE Melbourne
    Could this be solved by adding a 'normal' load to the circuit, something like a LV downlight or a 25W incandescant globe... that would absorb the leakage current without giving light output?
     
    ICS-GS, Aug 26, 2008
    #5
  6. phcjpp

    Htnut

    Joined:
    Aug 4, 2004
    Messages:
    97
    Likes Received:
    0
    Location:
    Sydney
    The Clipsal guys could confirm this but I would think that a 31CAP from clipsal could provide a path for the leakage current
     
    Htnut, Aug 26, 2008
    #6
  7. phcjpp

    phcjpp

    Joined:
    Oct 19, 2004
    Messages:
    112
    Likes Received:
    0
    Location:
    London
    All fixed - put a normal bulb in parallel.

    Thanks for the advice.

    Chris
     
    phcjpp, Aug 27, 2008
    #7
  8. phcjpp

    ICS-GS

    Joined:
    Nov 1, 2004
    Messages:
    347
    Likes Received:
    0
    Location:
    SE Melbourne
    don't you love it when simple things 'just' work :D
     
    ICS-GS, Aug 28, 2008
    #8