Level MMI status

Discussion in 'General Discussion' started by gumpyoung, May 30, 2011.

  1. gumpyoung

    gumpyoung

    Joined:
    May 26, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    Australia
    I've just done a program to parse CBus MMI with a CNI (firmware ver 4.6.0), I have no problem with group addresss ON/OFF status, but not the level MMI status.

    Got same result even when using CBus diagnostic utility : Can see the correct ON/OFF status for all the group addresses, but Level MMI shows none of the group address is presented.

    Checked the actual message responded from CNI, can see all level status is "0000", which means "NOT AVAILABLE" according to the documentation.

    Is it something to do with the dimmer installation?Or anything to do with the setup?
     
    gumpyoung, May 30, 2011
    #1
  2. gumpyoung

    gumpyoung

    Joined:
    May 26, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    Australia
    Just checked the firmware version of the dimmers, in "Unit Identification" page, the firmware version is "1.00",could it be the problem?

    If the firmware is 1.00, can I upgrade it(in software way)?
     
    gumpyoung, May 30, 2011
    #2
  3. gumpyoung

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    firmware version 1.00 did not support level MMI.

    No firmware upgrade is possible with these units; firmware 1.00 units are mask ROM devices.

    if you have any more recent output units (fw 1.3.0 +) on your network, and are not using all the output groups in any of them, you could put the same addresses used in your fw1.00 units in the free blocks of the more recent units. This way, the level MMI will be populated and operation of your network will not be otherwise affected.
     
    Don, May 30, 2011
    #3
  4. gumpyoung

    gumpyoung

    Joined:
    May 26, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    Australia
    Thanks

    Thank you very much Don.

    Will inform our technicians to replace the units.
     
    gumpyoung, May 30, 2011