Logic schedule issue

Discussion in 'C-Touch/HomeGate/SchedulePlus/PICED Software' started by LCC, Oct 14, 2006.

  1. LCC

    LCC

    Joined:
    Apr 13, 2006
    Messages:
    18
    Likes Received:
    0
    Hi all,

    Having trouble with a logic module that activates flashing lights when a scene is activated.

    I have a scene which turns all the AV equipment on and off which is operated when button on CTC is pushed.

    The logic compiles OK. When i have the CTC connected to c-bus on the PC via piced, the logic works fine on both the CTC and simulated on the piced. When i disconnect piced, it wont operate on the CTC.....????

    I have also noticed, that when i reopen piced and enter logic, this certain module always has the cross against it, whereas i have to enable it........

    Any ideas would be greatly appreciated!!!!!!!!1
     
    LCC, Oct 14, 2006
    #1
  2. LCC

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    This probably means that the code is not running in CTC at all and that it is PICED executing the logic.

    The cross means that the module has been disabled. There must be somewhere in your code where you have disabled it.
     
    Darren, Oct 16, 2006
    #2
  3. LCC

    LCC

    Joined:
    Apr 13, 2006
    Messages:
    18
    Likes Received:
    0
    Thanks, I found a disable command in the initialisation area, no idea how it got there!!! :D
     
    LCC, Oct 27, 2006
    #3