Low-voltage lighting equipment noise

Discussion in 'C-Bus Wired Hardware' started by sergeroz, Jun 14, 2007.

  1. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    I've had C-Bus installed at my home in beginning of 2006 (new home, and Yes, by a qualified electrician) in NSW, AUS.

    There are quite a few low voltage light fittings; some use manufacturer's magnetic transformers, and others have had them replaced with Possums (the green-yellow plastic ones). They are all connected to Dimmer modules like the L5508D1A.

    Here's the problem:
    • Light fittings with both electronic and magnetic transformers buzz terribly when dimmed to anything but 100% (loudest noise at ~10%-90% brightness). Oh, I'm quite certain that it is the transformers that generate the noise, not the 12V globes. And by terrible I mean almost the equivalent of, say, a pair of speakers connected to an amp with volume set near Maximum while nothing is being played: bzzzzzzz....
    • Furthermore, noise from some lights can be heard when they're switched OFF. It IS very quiet and can only be heard either with one's ear right next to the light fitting, or on a quiet night (I feel this necessary: I've had my ears checked AND the noise had been heard by another sane person).

    My electrician explained during installation that the Dimmers have Triacs in them and therefore there's always a potential in the wiring, and that nothing can be done about it. At that time I had no idea that I'd be able to hear light fittings buzz at night when they're switched off.

    I recently came across a good document on different types of low voltage dimmers (http://www.lutron.com/applicationnotes/362219b.pdf), and my suspicions have grown.

    I will be grateful if someone could authoritatively answer these few questions:
    - Noise = energy, so if the transformer of my downlight buzzes at night then I'm paying for that noise, right? And if I can hear some, then the others are draining current too, 24/7/365?
    - Are the L5508D1A Dimmers suitable for low-voltage lights (with magnetic or electronic transformers)?
    - If Yes, then should the light fittings have been connected in series through a similar DIN-style relay?
    - Should a different Dimmer module have been used, such as the Universal Dimmer? Have these Universal ones been on the market since December 2005?
     
    sergeroz, Jun 14, 2007
    #1
  2. sergeroz

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Yes.. all channels are doing it. You sparky is sort of right, the leakage is not due to the triac, but to the capacitor fitted across each channel for EMC compliance. This is in series with the lamp when the channel is off, so a small amount of current is always flowing through the load. The amount of energy that is wasted here is small, and as far as your hip pocket goes, it's mainly reactive power so you're not paying for it (in a domestic installation anyway.. as far as I know).

    Yes.. these dimmers use leading edge dimming, which is best suited to incandescent or iron core (magnetic) low voltage transformers. They can be used with electronic transformers, however there are limitations on the number of electronic transformers that can be put on one channel, due to the input capacitance of this type of transformer, and there can also be issues with buzzing. The buzzing issue is very dependent on the transformer itself.

    While some noise is normal with electronic transformers on leading edge dimmers, the amount you describe sounds unusual.. It's possible that the physical installation of your transformers might make the noise worse... for example if they're sitting on the top of the gyprock in your ceiling it can act as a sounding board and amplify the noise. There might be others here that can give you some other suggestions.

    This would obviously stop the small amount of noise when the channel is off, however it would seem like overkill to me. It's certainly not recommended as a standard installation technique.

    Ideally a dimmer capable of trailing edge dimming, such as the DIN Universal dimmer, would be used for electronic transformer loads. The DIN Universal Dimmer was not on the market at the time (they've been available for about a year now).

    Hope this helps,

    Nick
     
    Last edited by a moderator: Jun 15, 2007
    NickD, Jun 15, 2007
    #2
  3. sergeroz

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Some LV lamps and fittings are well known to buzz as well.

    In some cases the filament in the lamp is whats making the noise.
     
    ashleigh, Jun 15, 2007
    #3
  4. sergeroz

    Phil.H

    Joined:
    Jul 29, 2004
    Messages:
    466
    Likes Received:
    0
    Location:
    Sydney
    As Mr Ashleigh said,

    The light globes themselves (LV-Dichroic) act as a speaker for noise in the circuit. I have had a situaton was noise was an issue, - L5508D1A's and Tridonic iron core LV transformers, changed the globes to high quality units and got rid of 80% of the buzz. Electronics creates the noise cheap globes act as speakers in some instances ;)

    BTW where you say "AND the noise had been heard by another sane person" are you implying you are sane ? :D
     
    Last edited by a moderator: Jun 15, 2007
    Phil.H, Jun 15, 2007
    #4
  5. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    More questions

    Thank you for the replies posted so quickly.

    I have another question regarding the noise, prospective rather than retrospective this time: what should be done to remove (at least partially) the noise generated by light fittings when they are On and Off (these are 2 different problems, correct?)?

    The globes are all German-made 25W and 30W Osram HALOPINs (AC Mains) and HALOSTARs (12V DC). Light fittings with HALOPINs are very much silent at all times, so no complaints here.

    One wall light (that uses Osram 12V HALOSTAR globes) that hisses very quietly when Off (therefore noise must be coming from the magnetic transformer) is pretty much directly above a child's bed, and it just doesn't feel right to have it buzzing away at night. (Note, I'm not concerned with safety implications here, the light is more than reasonably high).

    Another light fitting, a downlight that also uses an Osram 12V HALOSTAR globe (with the light fitting's own reflector) can also be heard when switched Off. On this one, though, the transformer is the locally purchased Possum. I'm quite certain that it's the Possum that is generating the noise.
     
    sergeroz, Jun 15, 2007
    #5
  6. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    :mad: Well, not as much as I was BEFORE construction/electrical works!
     
    sergeroz, Jun 15, 2007
    #6
  7. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    Apologies for repetitive posting, but I made a mistake describing the transformer in the above post. The wall light has an electronic transformer as can be seen on this image.

    It can therefore be concluded that the C-Bus Dimmer modules and the electrical transformers don't like each other very much... How typical of technology :mad:.
     
    sergeroz, Jun 15, 2007
    #7
  8. sergeroz

    Phil.H

    Joined:
    Jul 29, 2004
    Messages:
    466
    Likes Received:
    0
    Location:
    Sydney
    If that transformer has metal parts or is mounted on a metal back plate (not sure from the pic) I would be putting a lug on that earth conductor and slipping it over the threaded metal post for safety reasons. You never know it might even help your noise issues. That transformer setup looks like trouble to me - just a gut feel... :)
     
    Phil.H, Jun 16, 2007
    #8
  9. sergeroz

    Custom

    Joined:
    Apr 7, 2005
    Messages:
    39
    Likes Received:
    0
    I?d have to agree with Phil.H the metal base plate in the pic should be earthed. There are single insulated conductors coming through a non-bushed cable entry, which could lead to some ?shocking experiences?.

    What is the lamp loading on the 105va transformer? I have seen some very erratic behavior on 2 x 50 watt up/down wall lights with 105va integral transformers when being dimmed. Dropping the lamps down to 35 or 20 watts has fixed the problem.
     
    Custom, Jun 16, 2007
    #9
  10. sergeroz

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    The most rigorous way to find where the noise is REALLY coming from is also the most time consuming and painful :(

    I'd suggest removing each lamp fitting from the surrounding whatever (gyproc, etc) and hanging it out by the cable. NOTE THIS COULD BE DANGEROUS!

    And also at the same time lift the relevant tranformer off whatever it is attached to and sit it on something that gives audible isolation - a piece of insulation bat or similar would probably do.

    Then turn the power back on and listen very carefully right alongside both the lamp fitting and the transformer. If you have a lot of other transformers / fittings doing the same thing then you will need to disconnect them to completely isolate them.

    This will tell you conclusively where the noise source is. Then you can take appropriate remedial action.

    NOTE: All this work should be carried out by a licensed electrician because you will *have* to go shifting / changing / disconnecting things attached to the mains

    JohnC - if you are out there reading, you know more about lamps than anybody else who contributes here - you might like to comment.
     
    ashleigh, Jun 16, 2007
    #10
  11. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    Removing the light fitting showed this:
    • All transformers seem to generate noise when light is Off. Without the fitting around it, I can hear a quiet buzz coming off it, (a different light fitting this time).
    • Only the transformer generates noise; the globes, and the whole fitting assembly are silent at all times.
    • Most of these light fittings ARE grounded, that one must be an 'oversight' by my electrician (I think he cut the cable too short and then couldn't be bothered).

    This transformer drives 4x 12V 20W Osram globes. Removing 1x globe does not remove the noise when light fitting is dimmed. Could the transformer be underloaded...?

    Any ideas on how to get rid of the noise when:
    1. Light fitting is Off
    2. Light fitting is dimmed

    Thanks for the help so far.
     
    sergeroz, Jun 16, 2007
    #11
  12. sergeroz

    Phil.H

    Joined:
    Jul 29, 2004
    Messages:
    466
    Likes Received:
    0
    Location:
    Sydney
    "He couldn't be bothered - that's ok then. I just hope a dangerous fault only ever happens on a unit that is earthed. :rolleyes:
     
    Phil.H, Jun 17, 2007
    #12
  13. sergeroz

    sergeroz

    Joined:
    Jun 14, 2007
    Messages:
    7
    Likes Received:
    0
    I am not going to leave it like this, I will get someone to fix it - you don't want me doing the work? Because I might be tempted to do the work without switching off any circuit breakers - too adventerous I am :).
     
    sergeroz, Jun 17, 2007