Measurement Application and Homegate

Discussion in 'General Discussion' started by mazeem, Jul 25, 2011.

  1. mazeem

    mazeem

    Joined:
    Jan 19, 2005
    Messages:
    8
    Likes Received:
    0
    Location:
    Kuwait
    I am trying to read temperature and Humidity values from a aqutek Th-10 "http://aqutek.asia/downloads/th-10.pdf" using General Input Unit 5504GI (version 4.3.00), the sensor provide values using 4-20ma loop. I have used
    the following steps to get the values into Homegate:

    The sensor is connected to channel 2 on the GIM and when I select the show current level I get some values.

    The Hysteresis is 1% and I have enabled the broadcasting on the Measurement Application and can see the broadcast in the application log as follows:

    DateTime= 7/25/2011 8:56:44 PM App= 228 Measurement Group= 004 Unit= 003 PC_GIM/GGINPUT Event= Device 4, Unit 3, Channel 1 - Value: 3.3e-2 Amps

    In Homegate
    Select Project->C-Bus Applications->Measurement Manager
    Click Add
    Name = Temperature
    Network = Main
    Device ID = 3 PC-GIM
    Channel = 1 (channel 2 of General input Unit /Temperature Sensor Channel
    Unit = oC [grayed]
    Click OK
    [No Current Value show in the Measurement Application Manager]

    I go to the Temperature Page and follow these steps:

    Component
    Place Tool
    Category = Measurement App
    Function = Real Value
    Channel = Temperature
    I get 0.0

    I also tried
    Component
    Place Level Indicator
    Select System IO tab
    Key Function = Status
    System IO Variable, In-built = Measurement App Real Value
    Value = 0 [grayed]
    Channel = Temperature

    Again I get 0.0

    I have tried the same using PICED with the same results

    And yes the Homegate is connected to the C-Bus, with green bar in the status bar

    What am I missing?
     
    mazeem, Jul 25, 2011
    #1
  2. mazeem

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Connect to C-Bus using the Diagnostic Utility and confirm that the messages you're getting from the GIM are actually what you are expecting. That will help isolate whether it's the configuration of Homegate or the PC_GIM that needs to change.
     
    Newman, Jul 25, 2011
    #2
  3. mazeem

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Do you see the messages in the HomeGate log?
     
    Darren, Jul 26, 2011
    #3
  4. mazeem

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    I believe that the problem is caused by confusion between Device Id and Unit Address.

    You have the unit (unit address 3) set to use Device Id 4, but in PICED, you have selected Device Id 3. In older versions of PICED, the Unit Types were listed in the Device Id drop-down list because people usually used Device Id = Unit Address. We decided that this was misleading (and has probably confused you in this case), so it was changed recently.

    In PICED, change the Device Id to 4 and it should work.
     
    Darren, Jul 26, 2011
    #4
  5. mazeem

    mazeem

    Joined:
    Jan 19, 2005
    Messages:
    8
    Likes Received:
    0
    Location:
    Kuwait
    Thank you Newman and Darren for the responses, and you are right Darren it is the Device ID, and you are right again that it is confusing, as I have a multi-sensor at address 4 and when I open the drop down list in the Measurement Application it says ?4 SENPILL? so I never thought to select it. So I have changed the device Id to 3 in the toolkit and I am getting some numbers.

    Now I need to convert the values from the GIM to real-world values and again I need some help. According to the sensor manual 0 degrees is 4mA and 50 degrees is 20mA; the GIM reports 26104 (34%) using the Show Current Level when the temperature is 29.8 degrees. What is the best way to convert the 26104 to 29.8?

    I have noticed that the scaling offset keeps going back to 4; is this a bug or it has to be 4?

    Thank you again both for your support.
     
    mazeem, Jul 26, 2011
    #5
  6. mazeem

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Don't pay too much attention to the Show Current Level in Toolkit initially. You're better off configuring the unit to broadcast messages regularly and looking at them in the PICED log or using the Diagnostic Utility.

    You should see messages on C-Bus that are all nicely formatted and scaled, according to the settings in the PC_GIM.
     
    Newman, Jul 26, 2011
    #6