Measurement Application

Discussion in 'C-Bus Toolkit and C-Gate Software' started by malpasi, Nov 6, 2013.

  1. malpasi

    malpasi

    Joined:
    Nov 10, 2004
    Messages:
    2
    Likes Received:
    0
    Location:
    Bristol, England
    I am trying to use the 5104DTSI temperature sensor to monitor the heat output from the back boiler of a wood burner and activate heating zones using logic in a PAC based on the temperature. When I set the sensor to use the ?measurement? application ($E4, 228), toolkit does not create the application in the tree. Deep in the forum I found a post from Newman in 2009 that hints this may be a problem with toolkit. Does anyone know if there is still a problem?
     
    malpasi, Nov 6, 2013
    #1
  2. malpasi

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Its not really a problem, as measurement application messages are used between sensors and devices-that-do-something-with-the-measurement.

    And toolkit does not know or understand or care about the information flowing in the measurement application. It configures a device to generate information in that application, or receive it. But it does not actually play in there itself.

    So I don't think this is a very big deal.
     
    ashleigh, Nov 7, 2013
    #2