Network Problem?

Discussion in 'C-Bus Toolkit and C-Gate Software' started by allgo, Oct 11, 2004.

  1. allgo

    allgo

    Joined:
    Aug 20, 2004
    Messages:
    39
    Likes Received:
    0
    I currently have a small network that I use for programming practice (one 8gang neo, 8ch dimmer, V2 minder and a 360degree pir). With switch and dimmmer connectted all is fine. Once the PIR is connected all control via switch is lost and load controlled via PIR is permanently on.
    Software/ Hardware burden no difference. But once I connect the C-Bus to Minder all is well again. The Minder does not have to be powered up, only connected via C-Bus terminals. Minder Burden not enabled. Any suggestions?
     
    allgo, Oct 11, 2004
    #1
  2. allgo

    MiniMe

    Joined:
    Jul 28, 2004
    Messages:
    26
    Likes Received:
    0
    Location:
    in a house
    my first guess would be that the Minder is the only unit with the clock enabled.
    Enable a clock in the Dimmer and see if that works
     
    MiniMe, Oct 11, 2004
    #2
  3. allgo

    allgo

    Joined:
    Aug 20, 2004
    Messages:
    39
    Likes Received:
    0
    Clock Enabled

    Clock in dimmer unit is enabled.
    Is it possible, that due to the PIR a second clock pulse is required.
     
    Last edited by a moderator: Oct 11, 2004
    allgo, Oct 11, 2004
    #3
  4. allgo

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Only 1 clock generator is required per network.
     
    Newman, Oct 12, 2004
    #4