network without PC interface

Discussion in 'C-Bus Wired Hardware' started by IRQ, Sep 9, 2005.

  1. IRQ

    IRQ

    Joined:
    Jul 14, 2005
    Messages:
    19
    Likes Received:
    0
    Location:
    Central Coast
    Hi,

    Can we have a c-bus network without PC interface? if Yes, how we connect to the network? Is there any other devices we can use for accessing the network.
     
    IRQ, Sep 9, 2005
    #1
  2. IRQ

    UncleDick

    Joined:
    Aug 5, 2004
    Messages:
    130
    Likes Received:
    0
    Location:
    Adelaide
    PC or not PC

    Yes you can have a C-bus network running without a PCI - you just need to make sure that one and one only Network Burden is enabled in a Relay or Dimmer unit or a hardware Burden is used and that at least 1 (max recommended 3) system clocks are enabled on relay or dimmer units on that network. This will give you a network that works but you will still need to connect a PCI to the network to program (via your PC - laptop) the switching associations, scenes etc that you want to occur. Now if you don't want to use a PC then you can program cirtain basic functions into the units on the network using the 'learn' feature.
     
    UncleDick, Sep 9, 2005
    #2
  3. IRQ

    Richo

    Joined:
    Jul 26, 2004
    Messages:
    1,257
    Likes Received:
    0
    Location:
    Adelaide
    If you don't want to use a serial PCI you can also connect to a network using a CBTI (Serial and modem connection), C-Touch B&W (Serial), PAC (USB) or CNI (Ethernet).
     
    Richo, Sep 9, 2005
    #3
  4. IRQ

    IRQ

    Joined:
    Jul 14, 2005
    Messages:
    19
    Likes Received:
    0
    Location:
    Central Coast
    So, if you wiring 10 units for example, as a standard, do you install PC interface for each unit, or just use on PC interface, to program (upload) the network, then remove the PC interface and use if for each network.
    (Here I am trying to save some money). what is standard practice?
     
    IRQ, Sep 11, 2005
    #4
  5. IRQ

    jay

    Joined:
    Nov 2, 2004
    Messages:
    51
    Likes Received:
    0
    Location:
    Brisbane
    You're on the money IRQ!
    We rarely install a PCI permanenlty in a job - it's not required after programming. If you need to access the network later, just take a PCI with you or if your network has any of the support units that Richo mentioned, do it that way.
    Cheers.
     
    jay, Sep 12, 2005
    #5