New Cbus Measurement Din Module.

Discussion in 'C-Bus Wired Hardware' started by Charlie Crackle, May 13, 2011.

  1. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Saw the Cbus Measurement device in the connected home MAG.

    The way I think you have implemented this is Great. 4 Channel Great IDEA. Split Core Great IDEA (I assume they come with it) Much easier to install. What is the ETA on this

    Looking forward to the Documentation.

    I have given up waiting on the EN40P


    Charles
     
    Last edited by a moderator: May 13, 2011
    Charlie Crackle, May 13, 2011
    #1
  2. Charlie Crackle

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    Hi Charles,

    Glad to hear it!

    I've had two of these installed at home as field trials for a few months now and it's certainly been an eye-opener.

    I expect we will cop some criticism for it not being a true power measurement (since it only measures current and derives power assuming a nominal line voltage and power factor.. both of which the installer can set for each channel), and for it not being an accumulation meter, but we believe it will addresses the needs of most, which is to give an accurate indication of how their power consumption varies with their behaviour, but not necessarily to predict the precise value of their next power bill.

    Nick
     
    NickD, May 13, 2011
    #2
  3. Charlie Crackle

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Thanks




    No, you buy each CT separately... i.e. Buy the Current Measurement Unit (CMU) as a part and the CT as a part. Both will be available at the same time

    Expected to be available Q3

    Will post the datasheet as soon as I can (just got back from CEDIA)
     
    Conformist, May 13, 2011
    #3
  4. Charlie Crackle

    znelbok

    Joined:
    Aug 3, 2004
    Messages:
    1,151
    Likes Received:
    17
    Shoul have gone to CEDIA Charlie - they had it on display there with the datasheets available as well. They ahd it running with the wiser widget and it looked great.

    I was under the impresison though that it was available now. Q3 is not that far away though so it wont be long.

    One question though, if I use this say on a small motor (lets say max 10A), and I have to use the 40A CT, how accurate will it be I am only using 1/4 the scale available.

    Mick
     
    znelbok, May 16, 2011
    #4
  5. Charlie Crackle

    NickD Moderator

    Joined:
    Nov 1, 2004
    Messages:
    1,427
    Likes Received:
    64
    Location:
    Adelaide
    In this case, if you have enough slack in your mains wiring, you can put multiple turns through the CT to get better resolution. The unit allows you to configure a scale factor for this so the numbers come out right.

    Nick
     
    NickD, May 16, 2011
    #5
  6. Charlie Crackle

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    If I understand correct this is a DIN rail C-Bus unit.
    Has nothing to do with the Wiser Home Energy Management System that is available in US.
    Is there at least a link for the "connected home MAG" to have a glance of this new product?
     
    2SC, May 16, 2011
    #6
  7. Charlie Crackle

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Datasheet attached
     

    Attached Files:

    Conformist, May 16, 2011
    #7
  8. Charlie Crackle

    bmerrick

    Joined:
    Jun 13, 2007
    Messages:
    437
    Likes Received:
    35
    Location:
    Sydney
    Any idea of RRP as yet? Also the CT transformers, assume they are similar to / slightly more than the Cent-A-Meter current sensors pricing?
     
    bmerrick, Jun 9, 2011
    #8
  9. Charlie Crackle

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia

    CMU is expected to be about $200 +GST
    CT's are expected to be about $25 +GST (each)
     
    Last edited by a moderator: Jun 10, 2011
    Conformist, Jun 9, 2011
    #9
  10. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    It the unit smart enought to know which way the current is flowing

    If you have unit measuing the Main Cable into the property and the property has a SOLAR system and can back feed the grid
    is the unit smart enought to know which way the current is flowing ?

    Will wiser handle this when the current goes the other way.


    Q3 is only 3 days away.... or is it the end of Q3 ??
     
    Charlie Crackle, Jun 28, 2011
    #10
  11. Charlie Crackle

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    No, you would need to put a CT on both incoming and outgoing separately.

    Good question... I don't think so (just had a quick look), but i might be wrong... I have been wrong once before. Oh wait a minute, no i'm wrong, i wasn't wrong that time.:rolleyes:

    q3...
     
    Conformist, Jun 28, 2011
    #11
  12. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Can we fix this in version 2?

    So are you saying you need to put two CT on the same cable
    do these CT have an arrow on them indicating direction of the current they measure. do they measure 0 when the current goes the other way



    So the answer is NO ? the graph it will produce will be consumption when it is not ? or will they go to 0

    Are we going to address this

    Charles
     
    Charlie Crackle, Jun 30, 2011
    #12
  13. Charlie Crackle

    Don

    Joined:
    Aug 4, 2004
    Messages:
    429
    Likes Received:
    0
    Location:
    Townsville, Australia
    The current measurement unit measures current the same way a clamp-on type ammeter does. Consequences of this are:
    1) only the ac component of current can be measured. dc current in the wire passing through the clamp will not contribute to the current level reported.
    2)phase information between the current and voltage waveforms is not known, so direction of power flow in the wire can not be determined
    3) there is no polarity on the current clamp. Ac current flowing either direction will display the same, and there is no way for the meter to determine the direction of current flow.
    3) power flow can be estimated accurately only with knowledge of the mains voltage and load power factor

    For your solar panel feed measurement, if you put separate clamp-on CTs:

    a) between solar panel inverter and grid connection, and
    b) between power meter and the loads, you should be able to work out what you're after.
     
    Don, Jun 30, 2011
    #13
  14. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Thanks don that makes sence I keep thinking DC when it is AC.

    how does my meter know which way the current is flowing !

    My cent-e-meter does not !
     
    Charlie Crackle, Jul 4, 2011
    #14
  15. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Does Tool Kit 1.11.8 mean that the

    Measurement SENCT4 is going to released for sale ?

    There are 9 days of Q3 left

    Charles
     
    Last edited by a moderator: Sep 21, 2011
    Charlie Crackle, Sep 21, 2011
    #15
  16. Charlie Crackle

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Yes
     
    Conformist, Sep 22, 2011
    #16
  17. Charlie Crackle

    Darren Senior Member

    Joined:
    Jul 29, 2004
    Messages:
    2,361
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Dealing with Solar Panels

    I have been trying out the new current sensors and it took me a little while to work out how to deal with solar panels. In my house, the power from the grid (P in the diagram below) joins the power from the solar panel (S) at a point which is not accessible.

    View attachment SolarFeedIn2.bmp

    It the diagram C is the power consumed by the house.

    Using Kirchhoff's Current Law, we know that:

    C = P + S

    So we can indirectly measure C by putting a current clamp around P and S as shown. Because C is always positive, P + S is also always positive and we don't need to worry about current direction.

    Similarly, S is always positive.

    P can be negative if S > C, but it doesn't matter since we are not measuring P by itself.

    Then in PICED, you can add the two Measurement Application channels for the two current sensors, but set the one measuring S to not be included in the totals (since the other current clamp is measuring the total C).

    I hope this makes sense. It took a while to convince myself that this was correct, and testing since then confirms that it works.
     
    Darren, Sep 24, 2011
    #17
  18. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Thank you darren for posting this.

    This is exactly what I was thinking but was not sure is PICED would cope

    Going to order my modules. Just having issues getting partnumbers for the current clamps
     
    Last edited by a moderator: Sep 24, 2011
    Charlie Crackle, Sep 24, 2011
    #18
  19. Charlie Crackle

    Charlie Crackle

    Joined:
    Aug 3, 2004
    Messages:
    815
    Likes Received:
    8
    Location:
    Melbourne
    Charlie Crackle, Sep 24, 2011
    #19
  20. Charlie Crackle

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Makes sense, Darren.

    I my case I had full access to P, C and S, so one channel does C directly, measuring actual power consumed by house (always positive) and another channel does S directly, measuring power from solar panels (always positive). The measurement channel S is marked as a generator in PICED so the nett consumption is simply the combination of these two measurement channels. The absolute value of P is not measured, nor would it be helpful anyway, as CT's cannot determine the direction of current flow, as P is negative whenever S is greater than C.

    The remaining measurement channels are used for measuring specific circuits of interest but are flagged not to be included in any totals in PICED.
     
    Newman, Sep 25, 2011