No network impedence/results showing.

Discussion in 'C-Bus Toolkit and C-Gate Software' started by ariddell, Jun 24, 2009.

  1. ariddell

    ariddell

    Joined:
    Apr 20, 2009
    Messages:
    58
    Likes Received:
    0
    Getting the info below on the wired part of our network, am sure it used to show the impedence value and confirmed 1 burden was required.

    Any ideas why it doesn't any more?

    stats.jpg

    Thanks

    Al
     
    ariddell, Jun 24, 2009
    #1
  2. ariddell

    froop

    Joined:
    Dec 23, 2007
    Messages:
    124
    Likes Received:
    0
    Location:
    Melbourne, Australia
    Can't say for sure if its the same for you, but I saw exactly the same a couple of weeks ago when I added an extra device to my network, which pushed the current supply over the edge. As soon as I removed the device, impedence was shown correctly.

    Make sure that your supply current is shown accurately. In my case, toolkit assumed that my two 12ch relays were power supply units, when in actual fact they weren't. So toolkit was reporting current supply of 1000mA when my network actually has only 600mA.

    You current supply is showing 400mA, which is more than likely made up of two relay and/or dimmer units, each with a 200mA supply. If you actually have only one unit with a power supply of 200mA, it is quite likely that it can still power your network even though it is calculated as requiring 244mA. But it may be unreliable.

    Mine runs fine with devices calculated at just over 700mA with only 600mA supply. But adding that one extra device pushed it over the edge.

    Did that all make sense? It's late in the afternoon and I'm not sure my brain is talking properly to my fingers..
     
    froop, Jun 24, 2009
    #2
  3. ariddell

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    It may be that you've got the C-Bus Cable (XC100B or XC305B) listed as items in your database. This can mistakenly make the impedance calculate as zero. This is a known issue and will be fixed in a future version of Toolkit.
     
    Newman, Jun 24, 2009
    #3
  4. ariddell

    daniel C-Busser Moderator

    Joined:
    Jul 26, 2004
    Messages:
    770
    Likes Received:
    21
    Location:
    Adelaide
    There is a known bug with impedance calculations I'm afraid (#17053) - it will be fixed in the next major release.

    I believe the following units might cause the total impedance to revert to zero:

    Cable (100m and 305m)
    Some of the North America Decorator style I/O units, catalog SLC58xxxxxUM, unittype WRDxRx
    Wireless Gateway, Wireless Remote Control units

    Do you have any of these in your project?
     
    Last edited by a moderator: Jun 24, 2009
    daniel, Jun 24, 2009
    #4
  5. ariddell

    ariddell

    Joined:
    Apr 20, 2009
    Messages:
    58
    Likes Received:
    0
    Thanks guys.

    Wireless gateway is the most likely one in this case then since we recently expanded out the system with a gateway and set of wireless switches at roughly the same time as the info disappeared.

    Power calculation is correct for the 2 dimmer units we have with PSUs, i manually set the model info on other units that were reporting as having PSUs in them but don't a while back after reading your thread at the time froop so all good on that front.

    All good, I won't worry about it in that case and hang off for future versions.

    Cheers,

    Al
     
    Last edited by a moderator: Jun 24, 2009
    ariddell, Jun 24, 2009
    #5