Outdoor PIR E5750WPL

Discussion in 'C-Bus Wired Hardware' started by Mike Costello, Apr 12, 2015.

  1. Mike Costello

    Mike Costello

    Joined:
    Dec 9, 2013
    Messages:
    47
    Likes Received:
    0
    Location:
    UK
    Hi,

    I've got a customer who really isn't keen on the E5750WPL outdoor PIR. I hear this often due to the looks of them.

    I had been told that I could use any PIR if I asked the electricians to install a twin and earth to give power and a CBus pink Cat5 back to the rest of the CBus and then linked to a L5504AUX 4 channel auxiliary input

    I now believe for this to work I need a outdoor PIR with volt free contacts. Please could someone advise if this is correct and if so if anyone know of a nice looking one in black.

    The only ones I've found so far are GJD sensors. Would these work?

    If anyone from CBus reads this the ideal solution would be for you to create a nice looking one. After speaking to other installers in the past this would be massively appreciated.

    Thanks
    Mike
     
    Mike Costello, Apr 12, 2015
    #1
  2. Mike Costello

    Roosta

    Joined:
    Nov 22, 2011
    Messages:
    560
    Likes Received:
    1
    Location:
    Australia
    My preference in this situation has always been to use the cbus sensor, however if the customer is particularly fussy as they can be I have successfully used the Clipsal 757SRR sensor with the 757FRM voltage free output relay for the sensor and a 5102BCLED cbus bus coupler..

    Its a fairly tidy looking unit which has some pretty good features..
     
    Roosta, Apr 13, 2015
    #2
  3. Mike Costello

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    787
    Likes Received:
    74
    Location:
    Adelaide, South Australia
    Hi Mike

    There are a couple of options.

    As you have suggested, using a unit with voltage-free contacts will provide a solution. You then feed the 'signal' (connection from the normally open voltage free contacts)to either a C-Bus Auxiliary input unit or a C-Bus bus-coupler. Deciding which C-Bus device to use will depend upon how close the C-Bus unit is to the voltage free relay (by 'how close', I mean the cable length from the contact to the unit and not the physical distance of the respective units). Under 1 metre, the bus-coupler will be OK. Over this distance, use the Auxiliary input unit.

    You could also have your electrician create a voltage free unit by feeding the output of the sensor into a mains relay and then take the signal from the relay contacts. The electrician will just need to make sure the sensor is the type that takes a neutral connection (3 wire design) as a 2 wire design probably won't drive just a relay coil.
     
    Conformist, Apr 14, 2015