Power supplies not suppling

Discussion in 'C-Bus Wired Hardware' started by BIZELECT, Oct 20, 2010.

  1. BIZELECT

    BIZELECT

    Joined:
    Oct 10, 2010
    Messages:
    4
    Likes Received:
    0
    Location:
    Adelaide
    I have two 200mA supplies (L5508D1A & L5508RVF), so I should have 400mA, available on the bus, but when I check out the network, I'm drawing 190mA and it says I've only got 200mA.

    Does this mean I've got a dead power supply or do they only turn on once the draw gets high enough?

    Oh, the whole system (except for this power issue) is working well....thanks Newman......
     
    BIZELECT, Oct 20, 2010
    #1
  2. BIZELECT

    tobex

    Joined:
    Nov 3, 2006
    Messages:
    728
    Likes Received:
    0
    Location:
    Sydney, Australia
    Stating the obvious, are the all power connections on the module in place ?

    When I first had DIN C-Bus I didnt connect the second power terminals to the first power terminals. That disabled the C-Bus power supply. Once I made both connections active the whole thing just worked.
     
    Last edited by a moderator: Oct 20, 2010
    tobex, Oct 20, 2010
    #2
  3. BIZELECT

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The calculation in Toolkit regarding how much power is available on the network is just that... a calculation. It uses the catalogue numbers entered in the unit UI's to determine whether the unit it is talking to has, or doesn't have, an in-built 200mA power supply.

    I suspect that one of the catalogue numbers for one of the units has a 'P' suffix, denoting it as passive, i.e. without in-built C-Bus Power Supply. If you correct this to reflect the actual units you have, it should calculate correctly.

    The power supplies current-share across the network. So, if you've got multiple supplies then each supply takes an approximate equal share of the load.
     
    Newman, Oct 20, 2010
    #3
  4. BIZELECT

    Duncan

    Joined:
    Jul 23, 2004
    Messages:
    925
    Likes Received:
    0
    Location:
    Salinas de Garci Mendoza, Bolivia
    Nice retrofit of a suitable "P" word for a poor catalog numbering decision :)

    Dunc.
     
    Duncan, Oct 21, 2010