Powerlink Breakers and Saturn Keypads

Discussion in 'General Discussion' started by wpimage, Nov 10, 2009.

  1. wpimage

    wpimage

    Joined:
    Nov 10, 2009
    Messages:
    3
    Likes Received:
    0
    Location:
    Indianapolis IN
    I was looking for a programming squence to operate a Square-D Powerlink Breaker with a Saturn Keypad or Saturn DLT.

    We have the Powerlink/C-Bus Device Router and NF3000G3C contoller in the Powerlink Panel. We are getting ready to install these.

    We have had no trouble setting up the C-Bus and operating the relays with the Saturn Keypads.

    Now we need to control a Powerlink breaker with the push of a Saturn Keypad button.

    What am I missing? What input or zone in the Powerlink Controller do I need to setup to recognize the addresses of the C-Bus keypads?

    For may Saturn keypad button 1:
    Key 1 Group: Shop Lights (which needs to control breakers 1,3,5,7)
    Function: On/Off
    C-Bus Address: 006

    For my Powerlink C-Bus Device Router:
    C-Bus Address: 007

    How do I take the info from my Saturn Keypad and operate the powerlink breakers on/off?

    What do I need to do in the NF3000GC3 controller to make it work? Zones/Inputs/...etc...

    Do I need to setup a Group Address under the Lighting Application in C-Bus Toolkit to control the Powerlink breakers?

    I hate to ask so many question on my first post.
     
    wpimage, Nov 10, 2009
    #1
  2. wpimage

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Reading through the Instruction Bulletin, it sounds like you need to associate a C-Bus Group number with an Input, associate breakers with a Zone and then link the Input to the Zone. You then need to learn all C-Bus inputs to that group, assuming they haven't already been programmed to use the correct group using Toolkit.

    There's a Quick Start guide on page 11 of the Instruction Bulletin. Does that provide any help?
     
    Newman, Nov 10, 2009
    #2
  3. wpimage

    wpimage

    Joined:
    Nov 10, 2009
    Messages:
    3
    Likes Received:
    0
    Location:
    Indianapolis IN
    I think we got it covered....for now. This is an interesting system I would like to use in a home in the future...
     
    wpimage, Nov 11, 2009
    #3
  4. wpimage

    wpimage

    Joined:
    Nov 10, 2009
    Messages:
    3
    Likes Received:
    0
    Location:
    Indianapolis IN
    Thanks for the link to those instructions. I don't think we had those. So far so good though!!!!! I will let ya'll know when something goes wrong.:rolleyes:
     
    wpimage, Nov 11, 2009
    #4
  5. wpimage

    Wire_Bug

    Joined:
    May 6, 2009
    Messages:
    22
    Likes Received:
    0
    Newman hit the nail on the head with his description of associating C-Bus Group Addresses to Inputs, then associating breakers with Zones, then linking those same Inputs with your Zones.

    Sounds like you've got it working, but let us know if you have any more problems.

    -John
     
    Wire_Bug, Nov 11, 2009