Programming bus couplers without scenes

Discussion in 'C-Bus Wired Hardware' started by 2SC, Apr 10, 2009.

  1. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    Can you help me please on this:

    In a hotel room when the energy save card triggers an old bus coupler (without scenes) I need to trigger a scene from a saturn switch.

    How can I do it?

    You have 6 hours ( I am going for sleep) :D
     
    2SC, Apr 10, 2009
    #1
  2. 2SC

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Put the old bus coupler in the Trigger Control application ($CA - hex), then set it up to either do a recall or issue an on or off.

    You can get it to issue a max of 4 scene triggers this way. This is the old, yuk way but it will work. You can't issue normal lighting commands though. It's trigger or lighting, but not both from the same unit.
     
    ashleigh, Apr 11, 2009
    #2
  3. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    Thank you Ashleigh but thats exactly what we did. After a better search we discover what the problem was.

    As I said a energy save card triggers an auxiliary contact that we used it to trigger 2 couplers in parallel. The auxiliary contact was closed as a card was in the card slot and opened a minute after the card was removed.

    The first coupler was for triggering a welcome scene on the local room network and the second one was for checking presence for the reception network.

    However, as we discover after a lot of testing and checking, even though the auxiliary contact was opened when we removed the energy card, couplers unexpectedly kept the same state. :eek:

    The problem was solved as soon as we installed a second auxiliary contact for the second coupler...:confused:

    Any ideas why this happened?
     
    2SC, Apr 12, 2009
    #3
  4. 2SC

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Sorry - no idea at all.

    Well.... maybe check the programming of the coupler carefully. Maybe it was set up so it did not send any commands when the contacts opened.
     
    ashleigh, Apr 13, 2009
    #4
  5. 2SC

    2SC

    Joined:
    Oct 10, 2006
    Messages:
    345
    Likes Received:
    0
    Location:
    Athens, Greece
    We didn't change anything on the programming. A small detail on the cabling and everything is OK.

    At first I thought that the problem occurred from the total length of the cabling to the couplers (no more than 10 meters) since the second coupler wasn't in the room.

    So I installed a second coupler next to the first one, but we had the same problem. As soon as we altered the connection (see attached pdf) everything run smoothly.

    I thought I should share it with you because sometimes when you are under stress trying to keep deadlines for commissioning it might be useful to someone else.
     

    Attached Files:

    2SC, Apr 13, 2009
    #5
  6. 2SC

    ashleigh Moderator

    Joined:
    Aug 4, 2004
    Messages:
    2,397
    Likes Received:
    26
    Location:
    Adelaide, South Australia
    Ah hah!

    You wired two bus couplers to the same contacts (in parallel).

    Do not do that, please !!!
     
    ashleigh, Apr 14, 2009
    #6
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.