    Scenario :

    Several NEO keypads controlling a number of Dimmer / Relay modules.

    We are trying to reconfgure (and fault find) an existing system.

    For example we have a dimmer "D1" on area "A1" with a single channel (a light) as group 1 "G1".

    We can't seem to ramp G1 (or any group) below about 40% brightness (at a 0% ramp it still is about 40%). There is no minimum set in the dimmer's settings. Only changing the area ramp seems to get around this.

    I'd rather specify a scene with individual ramps rather than ramping an area.

    What have I missed here?

    Cheers, Anton.
     
    factotum, Nov 13, 2012
    #1
  2. factotum

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    The first thing to check is that the correct messages are being sent over C-Bus. You can check this using the C-Bus Diagnostic Utility.

    The next thing to check is to be sure that the channel minimum/maximum values are set to 0% and 100% respectively.

    Check to make sure there aren't any logic groups associated with that channel as they may be affecting the minimum output value.

    Finally, it may be a factor of the load type. Things like dimmable CFL's can have very high minimum brightness levels, which is something they do to increase their compatibility with dimmers.
     
    Newman, Nov 20, 2012