Ramp time with Ramp to Level command

Discussion in 'C-Bus Serial Protocols' started by Conformist, May 15, 2006.

  1. Conformist

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    810
    Likes Received:
    91
    Location:
    Adelaide, South Australia
    Hi Guys

    A couple of questions if I may relating to the Ramp to Level command.

    If I set a ramp time of 8 seconds and ramp upwards, is the ramp time from the minumum level (0%) to the maximum level (100%) or from the current level (which may be anything) to the maximum level?

    The reason for my question is to do with proportional ramping. If I have a current level of 45% and I need to ramp upwards, will it take 8 seconds to reach 100% from the curent level or is there a calculation performed within C-Bus & make it 4.4 seconds (55% of 8 seconds)? This is quite important as I'm calculating the expected level internally and sending an instant 'Ramp to Level' when the user finishes ramping (ie on long release). I also us this for a memory dimmer function as well as requiring it for the pre V2 dimmers.

    Not sure if this is clear.... it's a little difficult to explain.

    Regards

    Chris
     
    Conformist, May 15, 2006
    #1
  2. Conformist

    Newman

    Joined:
    Aug 3, 2004
    Messages:
    2,203
    Likes Received:
    0
    Location:
    Adelaide, South Australia
    Conformist, I'm hearing you loud and clear!

    C-Bus ramp rates are defined for full range, i.e. 0% - 100%. This means that an 8 second ramp rate takes 8 seconds to ramp from 0% to 100%. Using this ramp rate and ramping from 50% to 100% would only take 4 seconds.

    This is the difference between a 'ramp time' and a 'ramp rate'. A ramp time is defined by the duration of ramping. A ramp rate is defined by the speed of ramping. For simplicity the ramp rates are expressed in seconds to ramp from 0% - 100%, to make it more lay-man friendly.

    The way this works is a fundamental aspect of the C-Bus communication protocol and can not be changed.
     
    Newman, May 15, 2006
    #2
  3. Conformist

    Conformist

    Joined:
    Aug 4, 2004
    Messages:
    810
    Likes Received:
    91
    Location:
    Adelaide, South Australia
    Thanks

    Explained very well.


    Cheers
     
    Conformist, May 15, 2006