Can a CBus system be fed via more than one RCD (residual current circuit breaker) e.g. one for each enclosure containing a number of CBus DIN rail units? If just one CBus network is involved (CBus cable daisy chained between all units in panel then on to next panel etc.) can it cause an imbalance and trip the RCD? Is it OK to feed the CBus control unit sides of dimmer / relay units in one enclosure via a first RCD, then for a second enclosure feed the CBus control unit sides via a second RCD etc. (with a common single CBus network). For CBus units in a particular enclosure, the control and power sides would probably be downstream of the same RCD. The existing setup of approx 85 circuits is fed by a single upstream RCD in the consumer unit which trips every week or two. However, when approx 60 percent or more of the circuits are turned on the RCD (not an RCBO) always trips out ? it does not seem particularly dependant on the actual circuits that are on (larger circuits may cause the tripping slightly sooner but it is difficult to tell). Note there are other circuits (not CBus) e.g ring main sockets, domestic kitchen equipment downstream of the same RCD but on a different MCB. The system is in a domestic installation in the UK, with a power supply of 230/240v a.c, 50 Hz, single phase. It was fitted by a Part P certified electrician (but they are not a CBus installer). The power supply to the building does fluctuate, when windy the light level varies, although the CBus system itself seems to cope well. CBus units are DIN rail dimmers and relays types L5508D1A, L5508D2A, L5512RVF (9 units supply power to CBus) There was a power cut and the RCD also tripped ? can the power supply quality cause an imbalance and trip an RCD? Any help is welcome e.g. redesign, fault finding, experience gained in this matter. More details of the setup and equipment can be provided if required.